Honeywell zone valve

RonV_2RonV_2 Posts: 32Member
When you open a Honeywell V8043G1018 motorized zone valve using the manual control on the bottom of the valve, (and lock it open by pushing the manual lever to its parking position) is the valve completely or only partially open?

Comments

  • STEVEusaPASTEVEusaPA Posts: 2,994Member
    depends

    if you de-energized before you slid the lever then yes.  If you moved it over, and it still has power to it, then probably no.
    steve
  • RonV_2RonV_2 Posts: 32Member
    edited September 2012
    double check

    My intention is to remove the function of the valve from my system by disconnecting its power source and then sliding the lever to the open position.  I understand that this would open the valve fully, is that right?
  • STEVEusaPASTEVEusaPA Posts: 2,994Member
    yes

    it should, unless theres some corrosion holding it open, but in that case you would know that already.
    steve
  • Empire_2Empire_2 Posts: 2,343Member
    HW zone valve.

    For all intent and purpose the valve is considered open when locking the cam.  There is only about an additional 1/8" if that of additional travel which if using the motor, it will stall in the open position with that extra 1/8".  Either way the ball is up and out of the way of flow for the most part.



    Mike T.
  • RonV_2RonV_2 Posts: 32Member
    thank you

    very much