mr
lmp
Member Posts: 1
Does it make sense to install a condensing boiler on a fan coil system in commercial applications?
0
Comments
-
it frequently can
Outdoor reset will have it condensing at least some of the time. A lot depends on the fluid temp requirement at design conditions (coil sizing.) System balance can make or break the job, so check the current conditions carefully. If there is a chronically under-heated zone it's only going to get worse if you lower the fluid temp.0 -
mr
But won't low water temps in the coil blow cool air? For boilers to condense they need water temps less than 130, right?0 -
Depends
You will always benefit from the turndown ratio of a mod/con. Matching the load will be more efficient than short cycling.
If you are designing a fan coil system from scratch you should be able to run it at low temps most of the time (outdoor reset).
If you are retrofitting an existing system you may get cool air at low temps.
Carl"If you can't explain it simply, you don't understand it well enough"
Albert Einstein0 -
that's exactly how we design them
Once a fluid temp is picked for the radiant system, we simply tell the coil sizer what there is. If the air system is on 100% of the time (mandatory air changes) the combination of outdoor reset and a proportionally-controlled coil valve frequently creates conditions where the LAT is only a degree or two different than the room temp. This allows lower water temps to have greater effectiveness than would be the case with a bang-bang thermostat driving a terminal unit.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements