Oil Hot Water Boiler Cycling

Options
Burntoacrisp
Burntoacrisp Member Posts: 20
1st post! Hello to all. I have a low volume oil hot water boiler, Dunkirk DPFO 3 section.

My question is currently, when there is a call for heat it will run for approximately 5-6 minutes before it hits the high and turn off. It will then fire again after water temp drops to set point for approximately 5 mins again to hit high. Is this acceptable? Should I drop a nozzle size to enable longer runs for more efficiency. It is my understanding that long continuous runs are more efficient. This is a newer well insulated home, outside temps 10-15 degrees during the cycles described above. Finned baseboard.

Thanks in advance to all who post!





Double post! Sorry!

Comments

  • Robert O'Brien
    Robert O'Brien Member Posts: 3,541
    Options
    Oversized

    It's oversized. A reset control will help with the cycling,I'd go with a Beckett AquaSmart,it's a direct replacement for the existing Honeywell control and can use a wireless outdoor sensor,the high limit diff is fully adjustable and that will help tremendously with the cycling.The firing rate can be dropped by someone who knows what they are doing and has a combustion analyzer. If it has a tankless coil,dropping the firing rate may adversely affect the DHW.
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Steamhead
    Steamhead Member Posts: 16,868
    Options
    Are you sure

    the circulator is working properly?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • Burntoacrisp
    Burntoacrisp Member Posts: 20
    Options
    Short Cycle

    It was installed with a indirect. It is currently not being used at all. So lowering the firing rate won't affect that. I have combustion analyzer to check the unit. The AFG will require a low fire baffle and new static plate. As for it being oversize the design temp is -30. And the indirect I'm sure was taken into account.  2000sf I'm getting pretty good efficiency, I would just like to wring out a little more!



    What is considered a "long run" vs a "short run"?
  • Burntoacrisp
    Burntoacrisp Member Posts: 20
    Options
    Circulator

     Yes, circulator cycles on/off  when it should.
  • Paul48
    Paul48 Member Posts: 4,469
    Options
    Micro-zones

    Is there multiple zones, and are they very small?
  • icesailor
    icesailor Member Posts: 7,265
    Options
    Cycling:

    I think that you might be stepping over a $10.00 bill to try to pick up a dime.

    There are a lot of oil burner technicians that claim that they can radically down-fire that unit and have it work fine. I've never been able to do that and I'm not one of them. Especially with an AFG. There's a limit to how low you can fire an oil burner and still have efficiency. At least that's my experience.

    Maybe with a Riello,,

    A little pet dander on the fan and it all goes out with the trash.

    IMO.
  • Wayne M. Lawrence
    Wayne M. Lawrence Member Posts: 19
    edited August 2012
    Options
    stack temp?

    Hi, I'm not familiar with this boiler, but curious. Is this a direct vent, or is a chimney used? If vented with a chimney, what is the stack temp? Is it an exterior chimney, is it lined? The stack temp in my opinion will determine what route you will have to take. Both short cycling, and extending the run cycle when downfiring will have adverse effects due to chimney condensation problems if the flue gas temp drops below dewpoint.
  • Burntoacrisp
    Burntoacrisp Member Posts: 20
    Options
    $10 for a dime

    I am leaning toward your opinion. I not so sure I want to go much lower. I am currently running a .65 @ 140psi giving me approx. .749 firing rate. If I drop lower I will have to move to FO head. So what does this mean? Maybe .50 to .75 increase in efficiency if I am lucky. Maybe a increase in condensation too. It is a direct vent with a short stack run. All this for an increase of maybe another minute of on time.
  • Burntoacrisp
    Burntoacrisp Member Posts: 20
    Options
    Zones

    No. All good size zones.
  • icesailor
    icesailor Member Posts: 7,265
    Options
    Short Cycling:

    I'd be more concerned with soot making up. Unless you have filtered the fuel to the max, and that includes two Garber Spin-On types and NOT, any canister types, those small nozzles under .75 GPH have a real propensity to clog up. Your 140# at the nozzle entrance will become .25 GPH at the outlet because of restriction through the strainer. Causing the temperature of the flame to drop, soot formation and high CO. And that $1,000+ digital combustion analyzer won't fix it. That's why you need one with a printer so that when you are done, you have an accurate record of what it was doing at the time you set it up. And when it goes down the toilet, and creates a huge problem, you can show that when it was set up, it was fine for your insurance company. Otherwise, it is like unprotected sex. You never know what you might get.

    In my experience.
  • Burntoacrisp
    Burntoacrisp Member Posts: 20
    Options
    icesailor

    Haha! I definitely would not want my boiler to get herpes! I have a wool felt filter at the tank and a Garber (10 micron) at the burner. So far so good with existing setup for past 10 years. I think I am going to stay with the existing setup. It works, so why mess with it for a dime? Thanks for your input and everybody else too!
  • Zman
    Zman Member Posts: 7,569
    Options
    6 per hour

    The number that is thrown around for short cycling is more than 6  per hour. You seem to be right about there. What is the differential between the boiler on vs boiler off? Stretching this number may be the easiest way to optimize you cycles. You want to be sure not to go so low that you impact performance or cause boiler condensing.It may be possible to combine this with Robert's suggestion of ODR.

    On a warm day you could run 150-170 and on cold day 170-190.

    Doubling your on off delta t will double your run time (almost).

    Carl
    "If you can't explain it simply, you don't understand it well enough"
    Albert Einstein