Re: Crowne Combination Boiler
Steve_210
Member Posts: 647
I have a Crowne combination boiler MWC116 for natural gas. We recently disconnected the Domestic hot water side and installed an indirect as tthe customer did not have enough hot water. Since then the relief valve started to weep at about 160 degrees. The pressure gauge on the boiler does not increase. That is what I am finding strange. If it were a blockage to the expansion tank or a bad expansion tank surely the pressure would increase. There is the possibiltiy of a bad gauage. Just wondering if anyone has come across this on these boilers or is there a common problem with these units?
Thank you
Thank you
0
Comments
-
Relief Valve
I'd try changing the relief valve first and see what happens.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Sorry
I forgot to mention I changed th reilef valve already0 -
Expansion Tank?
If the expansion tank was marginal, the extra water volume and higher temp required by the indirect may have tipped the scale against you.
Also, are you pumping away or toward the expansion tank?Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Check
the pressure with a gauge on the boiler drain.You may have to add another expansion tank in addition to the internal one.0 -
location
Without looking at the book and seeing how its piped in I am thinking you have to relocate the expansion tank, If the unit has a valve inside that closes/shifts due to priority then you have isolated the expansion tank from the indirect0 -
Crowne Combination Boiler
It's a combination boiler so the expansion tank is on the boiler but I am pumping away from the expansion tank. I will check the pressure with a new pressure gauge. It is possible that the one on the boiler is not working properly as it does not move when the water is heating. I don't think the unit can have any valve that closes or shifts due to priority. Again, it is a combination boiler. The brased plate heat exchanger has been made redundant. We are not using the Domestic hot water side of the combination boiler. I cannot see how the expansion tank could ever be isolated from the heating water but maybe I am missing something. I will check the pressure with an independant gauge.
Thanks again for all your help guys!0 -
ByPass
Check the by-pass piping in the boiler and make sure there is no obstruction. That boiler is a Basi Rivera rebranded.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements