scroll compressor
Paul_69
Member Posts: 251
will a scroll compressor pull down on a residential ac like the recipricating type?pump back into condenser? thx
0
Comments
-
Pull down?
Yes , a scroll will "pump down" if you front seat the king valve. But maybe/maybe not will pump down if you are talking a liquid line solenoid .0 -
scroll pump dpwn
thx techman. with new 410a equipment you must need to by pass low and high pressure switches it looks like to do this.0 -
hold on
.Bypassing the lo press control is one thing,but, bypassing the hi press control is a definate NO WAY! If you have that much 410a in the system that you are considering bypassing the hi side safety then you must first recover some of the freon ,then pump down the rest into the cond unit.You can stress out the copper/aluminum tubing and the comp by not knowing how much press you are creating.5lb of shoot in a 3lb bag.0 -
Paul
Not sure what or why you wish to pump down the system, but your mere questions are cause for concern. No Dis. intended, but only Professionals are qualified to work on any refrigeration system. It's not a do it your self er game. You can get seriously hurt! If you are an apprentice, have a pro over your shoulder while you are performing the procedures. This will make me feel better.
Peace
Mike T.0 -
pro
mike t., i have alot of experience in trade. i am new with 410a and scroll compressors. i am just asking general questions. i have a recovery machine etc.i recover when repairing . i just never tried to pull back into new style stuff. i for years did this with r22 systems and reciprocating compressors. i tried to pump down one unit with scroll like i would on reciprocating and it wouldnt pull down.like alot of techs there is always new stuff to learn and 410a is new to alot of us..ok. so i am asking questions because my first time i tried i couldnt get it to pump down with scroll type, so i recovered it and am just trying to figure what i might have done wrong or if it could be done.you cant know every new thing there is coming down the pike and i was here to seek advice so i could gain knowledge on this new style equipment.i would say this stuff is a learning curve for alot of expierenced techs and rookies. thx0 -
Appreciate your comment
Thanks for not taking it the wrong way. Believe me, I will be the first to say I don't know everything... Now I know. I just thought it might be a rookie and didn't want to see anyone hurt. Again I apologise. I am 28 yrs in the field and I try to help whenever possible. We are all here to listen and learn including Me.
Peace
Mike T.0 -
Pump down.
On AC cond(residential style) units there is no way to see what the cond coil press is when pumping down a system.No way to see what damage you are causing.When over stuffing a cond coil the hi side press is real hi, the comp is trying to push harder and pull what it can. At some point the comp can't push ,so it can't pull ,so it woun't pump down. Remove some freon and then there will be enough room for the rest of the freon to pump down into.Ever have an Amp meter on a comp when you over stuff a cond coil? Ever install a "tap valve" to see what those over stuffed press's are? But then you have to deal w/ removing the tap valve.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements