rinnai 75 combi mod range
jjwest
Member Posts: 6
in Gas Heating
Does anybody have an idea on the actual working modulation range of the ng Rinnai E75c? The unit I have always cuts out at about 25kbtu. The specs say it should go to 17kbtu. Is this normal for the Rinnai because of better combustion efficiency?
0
Comments
-
LP
If your boiler is hooked to Propane it will not go as low as natural gas.There was an error rendering this rich post.
0 -
Natural Gaz
Good guess, but no. It's NG. Is there any chance the computer thinks it's LP? The Rinnai tech laundry list hasn't found the problem yet so I was hoping for dumb mistake suggestions like "did you hook it up to propane?"0 -
Natural Gaz
Good guess, but no. It's NG. Is there any chance the computer thinks it's LP? The Rinnai tech laundry list hasn't found the problem yet so I was hoping for dumb mistake suggestions like "did you hook it up to propane?"0 -
Possible
It's possible, the conversion is a chip on the board and a orifice for the gas valve. It could have the wrong chip. The combustion numbers would be off if the orifice was in there. But the chip would keep it from modulating all the way down.There was an error rendering this rich post.
0 -
How are the gas pressures?
Aaron is correct on the chip/orifice, but gas pressures enter into this as well. Was this unit factory supplied as NG or converted?0 -
Another thing...
Check the min. Input setting in the set-up procedure. Perhaps the min setting was re-set to a higher number.0 -
Min mod setting
What parameter # is this?
Factory Gas
I'm going to get another meter.
Thanks0 -
Was speaking with a firend
and he suggested that you power it down and then up. The first thing that will show on start-up is the software version and it will show a 1 for ng or a P for propane. While unlikely perhaps there is a mix of orifiice/chip.
Min/max setting is parameter 3. Reading is in kw, so X 3414 for btu.0 -
Could the system just be under radiated?
I don't see the delta causing it to shut down instead of mod down, but maybe I'm wrong. It is the correct software version. I thought parameter 3 was only for max fire.? When parameter 3 is at its lowest setting, it does fire at 17kbtu.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements