3 zone FHW heat. Top floor zone always seems warm
kgssully
Member Posts: 5
in Gas Heating
Hello, I have a 3 floor colonial. Basement, 1st, top floors. Each on its own zone. For some reason when the other zones are running the top floor baseboards always seem to be warm as if the zone is on(but it's not). The zone pump is NOT running. The pumps are Taco IFC's. Could the check valve be stuck open and allowing flow no matter which zone is selected? The top floor zone does work normally when selected. Any ideas? Thanks in advance@
0
Comments
-
More Than Likely...
That's your problem. Look for some debris in the check of the offending zone.
If that doesn't correct it, post some pics of the near boiler piping, circs. and controls.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
That was it...
Found a tiny little piece of something sticking in it, causing it to stay open a crack. Nice easy fix. Thanks for the help!!!0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements