aquastat

davem1
davem1 Member Posts: 13
I went to replace a pressure relief valve on a burnham hot water system . I noticed that the water temp. was only 85 derees the aquastat was set to 180 and the burner did not fire they fired only when the the thermosstat called for heat  any ideas would be great

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,876
    On a hot water system

    the thermostat should control the circulator, not the burner -- and the aquastat the burner.  Check all your wiring, then if it's still no go check the controls themselves.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • davem1
    davem1 Member Posts: 13
    aquastat

    thanks for the reply. after speaking with a burnham rep i was told their gas boilers are cold start boilers which means that the aquastat does not maintain water temp. the reason why the relief valve is blowing off may be the expansion tank lost its charge