how to add a steam rad.

jonny88
jonny88 Member Posts: 1,139
hi,hope you can help.on the second floor i have a steam radiator .i am not allowed to open the floor.all that is visible is an 1.25 valve coming of a nipple and into the rad.my ? is can i remove the valve and put on a tee to pipe in another rad.i know dan says never to bullhead a tee.any suggestions would be appreciated

Comments

  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    Why a tee won't work.

    In a one-pipe system, the water has to flow back through the same pipe the steam enters through. That means the pipes and radiators have to be pitched towards the source. You can't pitch one side of a tee upwards without pitching the other side down.



    The good news is that you may not need to add a radiator. You might be able to make it heat up faster, and remain hot through more of the heating cycle, if you install a faster vent. By allowing the air to escape faster, it will fill with steam and start giving off heat sooner.



    If the radiator is undersize for the room it's in you might have to get a larger radiator. We can help yo figure out if it's big enough if you can send us a picture of the radiator tell us how tall it is, and give us the dimensions of the area it has to heat.
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • gerry gill
    gerry gill Member Posts: 3,078
    also,

    the pipe size is probably to small for two radiators..
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Hap_Hazzard
    Hap_Hazzard Member Posts: 2,846
    I was thinking that too.

    Increasing the EDR won't do any good if it isn't the limiting factor. If he ends up condensing the same amount of steam he'll get the same amount of heat no matter how many radiators or how big they are.



    Chances are whoever sized the radiator knew what they were doing, but whoever last replaced the air vent? Maybe not. Too many unknowns to say what the right solution is, but we can pretty much rule one out right away. ;-)
    Just another DIYer | King of Prussia, PA
    1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-24
  • jonny88
    jonny88 Member Posts: 1,139
    add a rad?

    thanks for your help.the reason for adding the radiator is that the new rad will be in the new closet and existing rad will be moved to other side of wall for a different radiator,the rad is original and works wonderful.i dont want to be the knucklehead who screws it up but my gut is saying not to do it.
  • crash2009
    crash2009 Member Posts: 1,484
    edited February 2012
    Johnny

     you need to know how many EDR's are connected to that 1.25" pipe right now.  Do you have Dan's book (tlaosh)?  Look on page 89, 1.25 riser will only handle 98 EDR.  1.25" runout will only handle 55 EDR.  You should also check the main to see if it can handle what you want to add.  If you check all that other stuff and still want to add a rad, this is one way to do it. 
  • jonny88
    jonny88 Member Posts: 1,139
    thanks crash

    the riser diagram you gave is very helpful thanks.sorry but i dont know how to draw up what i am trying to say,in reference to your diagram i would have to put a rad on each side of the riser,all i have right now is the valve,so i would be taking of the valve and i guess bullheading the tee to go on each side of the new wall,the new wall is bang in the centre of existing rad.thanks again for your help
  • crash2009
    crash2009 Member Posts: 1,484
    The first rad

     doesn't have to be on the left.
  • Jamie Hall
    Jamie Hall Member Posts: 24,862
    If the riser

    will handle both radiators, there is no harm to connecting two radiators to it with a T.  The problem with bull headed Ts is when you have two streams coming in on the cross bar -- one from each side -- and trying to take the flow out of the leg.  In this situation you would either be going in from the leg and out both sides of the cross bar, or in one cross bar and out the other and the leg.  No problem.



    You do want to be absolutely certain, though, that everything can drain.  With some ingenuity this can probably be done.



    What bothers me is... is this valve a right angle valve?  Maybe I'm missing something, but I sort of have the impression that you have a nipple coming up through the floor, into the valve, and the valve turns the flow at right angles and connects directly to the radiator.



    The problem is that if this is so, the connection to the radiator is probably a union, not a nipple, and half the union is solidly attached to the radiator as a radiator spud.  And I don't see any clever arrangement of fittings to get around that.  You can't just disconnect the radiator and valve and put a T in there!  More detail or description on that?
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,373
    need more fittings to make it work

    If you have the edr capacity on the riser you can turn the tee to a right angle to the wall with street 90's  pointing away from each other and 45's or street 45's to bring the sides inline with the radiator. The closet radiator I am assuming would be smaller so 1" may be enough to supply it. The radiators would then need to be straight pattern gate radiator valves.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • jonny88
    jonny88 Member Posts: 1,139
    mr hall

    you explained my exact situation.i have a right angled valve going directly into the rad,can i take it of and put on my tee????????