Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
24V to visionPRO for constant backlight
ChrisJ
Member Posts: 16,300
I'm considering running yet another fresh run of wire to my t-stat so I can have the constant backlight feature. My understanding is all it wants is 24V AC which I expect I can pull from the transformer that came with my WM EG-45 boiler by replacing my two wire run with a 3 wire run. I have a spool of 18AWG X4 handy so I might just use that.
My concern is that maybe this actually needs filtered DC and I missed a detail?
My concern is that maybe this actually needs filtered DC and I missed a detail?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Comments
-
Nope
Just 24 VAC for vision pro. I have a prestige that is lit up 24 x 7 running off my air handler xformer which is rusty and humms.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements