why the plumber connected the supply and return ends together
heatingFun
Member Posts: 84
Two yrs ago, we did oil to gas conversion. In the same time, we moved the boiler from one room to another. The main line is 1" pipe. In the old layout, the ends of the return and supply was not connected. The plumber connected the ends together during the conversion. There is no other changes related to the existing pipes. There is no other device/valve attached to the individual CI baseboards. Please have the look at the diagrams attached, or big version here, <a href="http://www.flickr.com/photos/bostonjames1980/sets/72157629021634185/detail/">http://www.flickr.com/photos/bostonjames1980/sets/72157629021634185/detail/</a>. The old Oil boiler is located at top right corner and the new Gas boiler is located at the bottom left corner.
The boiler loop in the new setting is recommended by the Burnham installation manual.
My questions are what's the difference if the ends are connected and the ends are not connected? and are they both 2-pipes direct return heating system?
The boiler loop in the new setting is recommended by the Burnham installation manual.
My questions are what's the difference if the ends are connected and the ends are not connected? and are they both 2-pipes direct return heating system?
1
Comments
-
0
-
Primary/Secondary Piping
Your plumber has piped your system pri/sec as is required by the manufacturer. Your second diagram is not correct as it is showing a bypass at the boiler.
The end of the loops should not be tied together unless you have TRV's on each rad and then there should be a pressure bypass valve at the cross over on the end. Another option would be a Delta P circ. in lieu of the pressure bypass if you have TRV's.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
I
need to read more carefully.As said, the loop should not be connected.0 -
second is the new setting
The second diagram is the new setting. the bypass in the boiler is recommended by the Burnham boiler installation manual.0 -
P/S piping
The boiler is piped somewhat correct. The installing contractor did get it pretty close but did not adhere to the distance before and after the closely spaced tee's. The returns and supplies should be tied together with the boiler tees located as is.0 -
Missed something?
Maybe I'm wrong on my understanding, but the first drawing/installation, whether primary/secondary is a direct return, with the supply and return not connected together except through the heat emitters or loops.
The second drawing/installation is primary/secondary with a direct return (NOT REVERSE RETURN) with the supply and return connected. Effectively changing the flow through the emitter/loops unless a ball valve is installed at the end if a differential by-pass is used.
I don't think that the installer knew what he was looking at.
In my opinion, a valve of some type belongs in the end to keep good flow through the emitters.
If it works, it works. If not, install a valve at the end.
Every time I see a direst return, I think of Mark Etherton's water skiing brother in law. going in circles.
A true reverse return may take longer and use more material but they sure do work well.0 -
Kinda thinking along same lines
Original piping being parallel piped where all heating loops will have same pressure drops, but different flow rates unless loops are identical so balance valves needed on each circuit.
With the new piping as Ice pointed out. The flow rates would be less through each loop because water is lazy, and stupid like another one of ME's x brother in laws. So whats to direct a decent flow into each loop, and keep the flow from just circling the secondary circuit. Not that there would be no flow in the loops, but maybe less. Before the flow was directed into each loop do to the pressure drop at the end of the last heating loop in the supply run.
Maybe I'm missing something, but usually the loops coming off the secondary piping have circs,zone valves, or TRVs for each circuit.
Gordy0 -
balancing act
i tend to agree with the valve at the end plan. the diagram doesn't really show if there were balancing valves of some sort included in the individual parallel heating loops which I assume the piping is largely undisturbed from the previous installation.
but presumably it more or less worked the way it was. because of the lazy water thing I would think a single valve where the mains connect would be a help. could definitely help get larger delta T to the boiler if it is condensing style.
Maybe the "bypass at the boiler was really diagramed as short primary loop as is common with low mass boilers and there was supposed to be close coupled tees (maybe they are) and additional circulator so that the primary secondary orginates at the boiler rather than having the mains as part of the primary loop.
jason. which set or sets of tees were you indicating you saw as violating proper P/S distances?0 -
I
believe he was refering to the changes in direction on either side of the closely spaced tee's above the boiler. He may have gotten the 4x's on the return but it doesn't appear he got the 8x's on the supply.0 -
picture is worth 1000 words
i was so busy looking at the diagrams i didn't look at the picture.
it is hard for me to get a grip on whether the primary rounding two corners between the secondary connections means that the theoretical drop is increased between the tees more than desirable although they are close coupled. Is that the reference to not quite close enough?
i admit to perplexity at the 4x and 8x reference.
Sticking to the valve idea between end of secondary feed and return (or no connection as it used to be running in the opposite direction.
brian0 -
That's
4 or 8 times the diameter of the primary pipe.0 -
more info is here
1. There is no any control valve for each IC baseboard.
2. The main line is 1" pipe and the size to IC baseboard is 0.5", I think.0 -
here's my .02
Those emitters are connected to those1" main supply/return lines with regular tees, not monoflow. There is nothing that is going to make water flow in them with the mains being tied in at the end.
While they are capped or valved "off", the flow has no choice but to go in the emitters, however I am not a big fan of this 2-pipe system. Especially when you are talking about cast iron rads. Water being lazy, will want to flow thru the easiest loops and any at the end of line will have a difficult time heating up unless valves are regulated to balance the flow thru closest emitters near the boiler.
The return pipe, will not see any temp rise until the emitter is warm, which with large cast iron rads, can take a while. So you have to be concerned with condensing in an atmospheric boiler unless you have a bypass set up or primary/sec like in that pic.
The OP must have some concerns or wouldn't be posting on here, is the heat output less with this new system?0 -
Reverse return
If there is a problem or a worry, I would disconnect the return at the last return tee before the boiler and cap the 1". Disconnect the by-pass connection and connect the return after the last/first loop and run the 1" back to the old return on the boiler.
That should make that lazy butt brother in law earn his keep.
IMO,0 -
That's..
what I would do. First emitter on the supply is the last one on the return. All heat even and at the same time.0 -
ok now im really confused on the 4x and 8x
i've seen reference to multiples of the pipe diameter for spacing of tees but I don't understand how you could have different spacing for the supply and return because that is the spacing we're talking about. it would be the same for supply and return, but maybe I'm missing something.
actually, looking at the picture again, and remembering that water takes the path of least resistance I question the wisdom of the otherwise convenient and clever use of straight through piping on the secondary loop. While the spacing of the tees is close, the corners effectively add to the spacing maybe making it too large.
like the diagram for reversing the return and taking out the bypass albeit to clarify that is the bypass at the outer end of the loops not the bypass that is the primary loop.
this is clearly what was suggested by the diagram but just to make the language match.
brian0 -
That's
That 'il git 'er dun.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements