Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Stewart Warner Corp Winkler G-200N
rlenr
Member Posts: 1
in Gas Heating
The pilot is not relighting. There is a General Controls gas check value and I am wondering how to test it. The whole works are about 30 years old.
0
Comments
-
Is this a thermocouple
type pilot? If so go to "RESOURCES/LIBRARY" above and click on Tim McElwains Closet for procedure to test thermocouples along with charts to chart out the readings.
The valve by the way is not a check valve it is a gas valve, probably a pilot safety valve.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements