Stewart Warner Corp Winkler G-200N
rlenr
Member Posts: 1
in Gas Heating
The pilot is not relighting. There is a General Controls gas check value and I am wondering how to test it. The whole works are about 30 years old.
0
Comments
-
Is this a thermocouple
type pilot? If so go to "RESOURCES/LIBRARY" above and click on Tim McElwains Closet for procedure to test thermocouples along with charts to chart out the readings.
The valve by the way is not a check valve it is a gas valve, probably a pilot safety valve.0
This discussion has been closed.