Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Backflow preventers

Options
Rttplumber
Rttplumber Member Posts: 1
My customer has a gas fired steam boiler with a condensate tank. The rpz drips water and now the boiler is short cycling. I have the pressuretrol set at 6 psi and its reaching that quickly. Any input would help. I'm confused

Comments

  • Ironman
    Ironman Member Posts: 7,376
    Options
    First...

    I would recommend that you move this thread to the"Strictly Steam" forum. You'll get more responses there.



    Second, set the pressuretrol down to 1 psi or less. The system doesn't need any more than that and setting it too high actually causes it to heat slower and creates other issues.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
This discussion has been closed.