vacuum breaker

targetman
Member Posts: 105
Our company substituted hoffan #75 air vents for vacuum breakers. This is on a steam coil in a Trane air handler. What problems could I expect to see if any?
0
Comments
-
The question
really is, what is the steam pressure the air handler runs at? If the Hoffmanns are rated for that pressure, I don't see why there would be a problem. The 75 is rated for 3 psig; the 75H is rated for higher pressures.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0