Copper Underground condensate return - expansion joint needed?
elfie
Member Posts: 266
have a 50 foot underground copper condensate return line that began to leak at the expansion joint.
it was an older expansion joint not rated for steam
is there a need for an expansion joint (what is common practice?)
is there a recommended expansion joint 1 1/4 inch that would be appropriate?
i tried to order a steam rate expansion joint and it had to be a custom built joint (ie. not off the shelf which seems odd)
thanks
thanks
expansion joint
there should not be steam in the condensate return line--only hot water.--nbc0 -
Agreed...
after a fashion. If this is in fact a wet return -- which if it is underground I expect it is -- there should always be water in it, and you can probably get away with an expansion joint rated for hot water.
I apologise if my previous comment on this issue was a little misleading; I hadn't quite added up that this would probably be a wet return.Br. Jamie, osb
underground return is dry
this underground return is not wet as it appears to slope downward into a condensate receiver.
so its a dry underground return that is at risk for steam flow0