Burnham alpine
niffa59
niffa59 Member Posts: 1
Just received a call back from a customer regarding a Burnham alpine.model alp-150
The boiler is making a humming noise when the gas valve opens up.
I have adjusted the throttle screw on the gas valve and seemed to help ,but has
not solved the problem completley.
Any suggestions would help
  • furnacefigher15
    furnacefigher15 Member Posts: 514
    Did you
    Did you do a combustion analysis?
    What throttling screw? gas pressure adjustment?
  • Tim McElwain
    Tim McElwain Member Posts: 4,651
    Has this unit
    had the up grade from Burnham for the Alpine? If not contact them and get the information.
  • Jason_13
    Jason_13 Member Posts: 305
    Upgrade
    What Alpine update are you talking about?
  • Tim McElwain
    They had some problems with
    a Series of Sage controls if I am not mistaken. They also have a product bulletin dated Nov 19, 2010 about LCD Displays and Ignitors.
    It is product bulletin #103398-01R1 of Nov 19, 2010.
    Other things to check:
    1. Make sure the gas pressure does not drop more than 1" W.C. when the gas valve opens
    2. Verify the gap on the igniter
    3. Adjust the O2 to 5.6 - 6.1
    4. Verify the gas line is over 10 feet long from the meter.
    If none of the above works lower the max heating fan speed by 500 RPM's and readjust the O2 to the above specs.
    If none of that works contact Burnham