Bouncing vapor gauge
Abracadabra
Member Posts: 1,948
Please see youtube video I link to below. Turn down your volume. It's a big power burner. Is it normal for a gauge to be bouncing this much? This happened after I significantly increased the venting on the main (as in completely removed the main vent). Prior to the venting increase the gauge would read properly and cycle between 4 and 12 oz. (hi/lo burner). New gauge.
<a href="http://www.youtube.com/watch?v=Qwm0g3o9qqI">http://www.youtube.com/watch?v=Qwm0g3o9qqI</a>
<a href="http://www.youtube.com/watch?v=Qwm0g3o9qqI">http://www.youtube.com/watch?v=Qwm0g3o9qqI</a>
0
Comments
-
Great video!
The video shows exactly how ineffective the standard gauge is at the lower pressures needed for our systems!
If that was taken during the venting phase, I would say that your main venting is still not adequate. Add main vents until your gauge shows 1 ounce back-pressure, and yes there is bound to be some jumping of the needle at these low pressures. Some people (including myself) have put snubbers on the gauge, but I now have taken mine off, thinking that it's like swimming in your overcoat( snubs too much).--NBC0 -
can't add more venting...
.. maybe i should add a vacuum pump ;-)
nbc, I can't add any more venting. It was a completely open pipe when I was running that.0 -
Gauge Snubber
Hi- I was going to suggest a gauge snubber
Ray Gauge Snubber
http://www.valvestore.com/products.asp?dept=1122
Porous for Steam - Part # 32627 - 1/4 “ NPT Stainless
- Part # 32618 - 1/4 “ NPT Brass
though I see NBC isn't overly enamored with them.so you might want to discuss it more with him. I used one on a friend's vaporstat which was oscillating a lot.
- Rod0 -
Open vent still constipated?
I am amazed that the back-pressure isn't lower with an open pipe. One of the old sales brochures in the archives here had a pitch such as,"nothing can vent the air from the system better than an open pipe", and the vent pipe went up the chimney.
As far as snubbers, don't just follow my remarks as it was a gut feeling.--nbc0 -
-
My $.02
on snubbers -- they do damp the swings a lot, and it really depends on what you are trying to do and how the whole thing is set up. I like to have them on vapourstats, particularly when they are set very low, as they eliminate false trips from small pressure blips -- and what you are trying to do with them is control on the average pressure. If your cutout is set at, say 6 ounces, and the blips are plus or minus an ounce, a snubber would help a lot. On the other hand, if you cutour is set at perhaps 16 ounces, they don't make such a difference...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
snubbers
I'm curious if you have since installed a snubber and if so how much did it help?
On another note, whenever I open up a layout and vents are labeled "V1, V2" and so on it confuses me every time. I work a lot with vacuum tubes and schematics always have tubes labeled in the same way. It does make me laugh after the few seconds of "duh".Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
snubber
nope, no snubber. With the main vents on, the bouncing is decreased quite a bit.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements