Pressure Gauge Concern.
cunam
Member Posts: 13
<span>
Hello!
I'm using Burnham steam gas boiler.My question is about the pressure gauge,because no matter how cold outside,the system running all the time but the pressure gauge won't move a bit,is it a problem?My boiler is 1 year old and the main control set at 2 psi and the DIFF is 0.75 psi.Thank you for your help.</span>
Hello!
I'm using Burnham steam gas boiler.My question is about the pressure gauge,because no matter how cold outside,the system running all the time but the pressure gauge won't move a bit,is it a problem?My boiler is 1 year old and the main control set at 2 psi and the DIFF is 0.75 psi.Thank you for your help.</span>
0
Comments
-
That's normal
You have the required (by insurance, if not by code) 0 to30 psi gauge. Those things are just about useless at normal residential steam pressures -- they just don't respond accurately, if at all, at 0 to 2 psi.
If you really want to know the pressure your system is operating at -- and it is probably in the range of a few ounces per square inch -- you need to add a 0 to 3 psi gauge.
And, incidentally, check what the pressure control is set at. If it is the common "additive" pressuretrol, the cut in should be set a about 0.7 to 1 psi, and the differential at no more than 1; if it is the subtractive type, then the cutout should be set at about 1.5, and the differential at 1. If it will go that low...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Thank You.
Thanks for your reply,just one more question please.How to know if the main steam vent working properly? Because I have two at the basement for around ten years already.Thanks.0 -
Several ways to check a vent...
the simplest is when the boiler starts to make steam, feel at the opening on the vent -- you should feel air coming out (if not hear it). It can be difficult to feel... Second, if the steam reaches the end of the main fairly quickly -- a matter of a few minutes (I've sort of use a rule of thumb of about 1 minute for 15 feet of main -- but that's just a ballpark) the air is surely going somewhere... most likely out the vent!
And, of couse, when steam gets to the vent it should close -- no more air or steam.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
You are the man.
I like you already.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 98 Geothermal
- 155 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 909 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements