Build your own rad?

Scot B
Scot B Member Posts: 26
I did a quick search but found no compatible results, so I'm asking for some assistance.  I have a small room that I would like to put a rad in for a one pipe steam system, however all existing rads are to big.  The room has deep door mouldings and a pipe radiator would work perfect. It's a utlility room so looks are not a concern. Is there a resource to guide me in building a pipe rad in regards to pipe diameter, height, pitch, venting requirements and fitting specs?  Has any one built one?

The room is 4x8 with 10 foot ceiling. One 32x72 inch window with two outside walls. Well insulated.  Why? I want it warmer in that room and I wanna play with the system.  I'm curious. Plus it would look cool!

Thanks for any help!

There was an error rendering this rich post.

Comments

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    edited January 2012
    pipe radiator

    i made a vertical pipe radiator from 1 in pipe on top of a full port 1 in. ball valve. i put the air vent at the top using various fittings, which kept the vent vertical. if i were to do it again, i would use a larger diameter pipe with a smaller one inside, to give more thermal mass. you could try various diameters and see which sizes fit inside another.

    maybe 2 vertical pipes, joined at the top, and bottom, would give better results.--nbc
  • Scot B
    Scot B Member Posts: 26
    edited January 2012
    smaller inside larger?

    Would the inner pipe be attached or threaded somehow or just sit loose inside? Would probably have to cut notches in end of inner pipe to allow condensate and steam to pass around and through it.

    If joining pipes at bottom and top, do they make a left and right handed threaded fitting to avoid a union?

    There was an error rendering this rich post.

  • nicholas bonham-carter
    nicholas bonham-carter Member Posts: 8,578
    pipe rad

    i was thinking of the inner pipe being loose, and a union would be required for a double pipe, joined at the top and bottom.

    just go down to the hardware store, and see how the different diameters fit inside one another. some wire would also work to increase the mass.--nbc
  • Jamie Hall
    Jamie Hall Member Posts: 24,518
    And you can estimate

    the amount of pipe you need -- figure the heat loss of the room, and remembering the 240 BTU per square foot -- EDR -- rule, just divide the heat loss by 240 and there's your area.  The area of the pipe, of course, is the length (in feet) times pi (3.14) times the diameter -- converted to feet, and the real outside diameter!



    Need more length?  Double it back on itself... or triple... or whatever.  Just remember that the condensate needs to drain out, and the vent needs to allow all the air out!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • crash2009
    crash2009 Member Posts: 1,484
    edited January 2012
    Pipe Coil

    Sounds like what you are looking for is something called a "pipe coil"  There is some info up in the library here.  Here is a flyer to get you started.  http://www.heatinghelp.com/files/articles/1258/498.pdf  see page 6
  • gerry gill
    gerry gill Member Posts: 3,078
    first find the heat loss in btu/hr

    then pick a pipe coil size (diameter) and consult the chart thats in the library here that gives heat output in btu per linear feet of pipe, and build your coil. Think like steam, and imagine your the condensate, can you drain out okay? Be best to pipe it two pipe fashion. Study up on pipe coils as they come in different designs, any of which may fit your application. Hope that helps.
    gwgillplumbingandheating.com
    Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.

  • Scot B
    Scot B Member Posts: 26
    Awesome!

    Thanks for your help! Still the best site on the internet!

    There was an error rendering this rich post.

  • crash2009
    crash2009 Member Posts: 1,484
    BTU calculator for horizontal pipe

    Scot, after you do the heatloss for the room, this calculator might be able to tell you how many lineal feet of pipe you will need.  Would be interesting to know if the charts up in the library match a computer calculator.  http://wbdg.org/design/midg_design_echp.php