honeywell pressuretrol
TonyG
Member Posts: 4
I want to ask you guys,,,how does this honeywell pressuretrol 404 f
1367 setup works,, ,where it says that the DIFF “Differential is
Subtractive” what do it means,,,,that if you have MAIN,,,,lets say at
3 psi,,,you have to set the DIFF at 1.5,,,or if you have Main at
2,,,them DIFF will be 1,,,or if you put Main at 1 them DIFF be
.5,,,is this how is when the say “Differential is Subtractive” is thats
the way or I am wrong???
1367 setup works,, ,where it says that the DIFF “Differential is
Subtractive” what do it means,,,,that if you have MAIN,,,,lets say at
3 psi,,,you have to set the DIFF at 1.5,,,or if you have Main at
2,,,them DIFF will be 1,,,or if you put Main at 1 them DIFF be
.5,,,is this how is when the say “Differential is Subtractive” is thats
the way or I am wrong???
0
Comments
-
Diff subtractive
Example Diff set at .5
set point 3
means switch on at 2.5 and off at 3.50 -
thank you for your reply furnacefigher15
Diff subtractive
Example Diff set at .5
set point 3
means switch on at 2.5 and off at 3.5
on that example that you gave me ,,, If I put that Diff at .5 like you say,,,set point 3,,,,what's the set point,,,the Main?,,,,and how do you get to those numbers switch on at 2.5 and of at 3.5,,,that's what I what to learn ,,,I really appreciate if you could explain to me in a easier way and I thank you for your time,,thanks0 -
thank you furnacefigher15
Diff subtractive
Example Diff set at .5
set point 3
means switch on at 2.5 and off at 3.5
Reply
is this what you mean,,,by if Diff is at .5 and
set point at 3,
is like subtracting 5 at switch on
and it adds 5 at off ?
I think I starting to understand ,,,what you saying0 -
Does not add
If the differential is subtractive, it does not add to the main setpoint. For example, if the main is set to 3 PSI and the differential is 1, then the control will cut out at 3 PSI and cut back in at 2 PSI. ( 3 -1 = 2 ) The differential does not affect the main setting, only the pressure at which it cuts back in.0 -
My mistake
Mike is correct
Subtractive differential only effects cut in point.
set point is all ways the cut out point and the cut in is the cut out minus the differential.
so set point 5 psi is the cut out point
differential of 1 would cause a cut in at 4 psi.
I need to stop giving answers this late at night.
Tony, the example I gave before is for standard differential (say for a residential thermostat)0 -
If using a standard
P 404 pressuretrol we would want it to shut off at 1.5 to 2 lbs and back on at .5 that is typical for a residential steam system using that pressuretrol.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements