steam gas boiler shutoff pressure
philg
Member Posts: 4
Is it normal for the pressure cutoff on a gas steam heat unit to vary between
6psi and 10psi when the thermostat setting remains constant?
Thanks,
Phil Gribbins
6psi and 10psi when the thermostat setting remains constant?
Thanks,
Phil Gribbins
0
Comments
-
Gauge?
A steam system should never go over 1.5 to 2PSI and much less than 1PSI is better if the controls allow it.
Are you sure the gauge is working, does it read zero when cold?
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
In a word,
No.
As BobC says -- are you reasonably sure the gauge is working? They sometimes get tired.
Second question: what is the pressurestat set at? For any residential system -- indeed even for most really big systems -- it should be set to cut out at not more than 1.5 psi, and less is better.
Things to check: is the pressurestat working? Is the gauge working? Are the pigtails to the pressurestat and the gauge open?
You may need to add a separate low pressure (0 to 3 psi) gauge to the system -- but note that your insurance (and most codes) require that you keep the 0 to 30 psi gauge, too.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements