In-Wall Fin Tube Convectors Noisy
nz
Member Posts: 125
I have a 1930 home with a two pipe steam system. The first floor has mostly in-wall radiators. Based on my reading and observations, they seem to be a fin-tube style convector. There is a grill on the bottom and in the middle of the wall. The middle of the wall grill has a damper. I have attached a photo of one of the radiators, there are nine of them. They are varying sizes, from 24" to 48".
When the steam reaches these radiators, there is a clinking noise as they warm up. It is not water hammer, I know what that sounds like :)
Also, the noise is evident (but the clinks are farther apart in time) as the radiators cool off.
Is there something that can be done to stop the noise?
When the steam reaches these radiators, there is a clinking noise as they warm up. It is not water hammer, I know what that sounds like :)
Also, the noise is evident (but the clinks are farther apart in time) as the radiators cool off.
Is there something that can be done to stop the noise?
0
Comments
-
Expansion
noise. You may be able to do something about it if you take the covers off and take a look at how the tubing is supported. It may be possible to put some slippery tape under the tubing on the supports, and that might help. No guarantees...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Noise
Jamie - thank you.
I should have described the sound better. It sounds like every single fin in each radiator makes a noise - so its not just one "clink" - but about 40-50 "clinks" per radiator. So I'm led to believe that its the fins making the noise, not the actual pipe shifting (although that might happen as well, I can't hear it over the all the "clinks")
I'm not sure if we can post WAV files here, but I'll try to record the sound when I get home and post it later.0 -
Fins
One of the dependencies -- a small cottage -- on this monstrosity I care for has electric baseboard heat (which we rarely use, thank goodness) which has fins, just like your fin tube units. They clink, so I know just what you mean. Drives one nuts. But it is the expansion of the unit (or in your case, the tube) which does it -- it sticks and slips on its supports, and every time it slips the fins "ring" with the vibration.
I admit I haven't been able to fix it -- although I got it much better with the slippery tape.
I sympathise, and good luck!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
It may be that the finned element
is rubbing the side of the sheet metal box of the invisible radiator unit..try removing the lower grille and looking up with a mirror to see what your doing and see if you can shift the element some.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Fin Tube Noise
I recall spending time in a friends house many years ago. The house was built new in the early 1960s. It had hot water baseboard heat, the first that I had ever seen. It was great, no drafts, no fan, and the location of the baseboard blanketed the cold exterior walls and windows with a very soft heat. But, when the pump came on and started to circulate the hot water... it was a chorus of clinking! I know that they later were able to make the 3/4" copper fintube element much quieter. Having operated a school building in the early 80s, I can also say that many of the convectors that we had in the building clinked alot, and others were nearly silent.
I would follow Jamie's advice and see if you can improve things. You will probably not achieve total silence. But, it will be worth the effort.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
expansion noise
This may not be practical for you.
I have a heating zone with fin-tube baseboard in it. Fortunately for me, I have a mod-con boiler with outdoor reset. I have the reset curve set very close to the actual heat loss of the zone it is in. So instead of turning 180F water on and off to maintain the desired temperature, the boiler modulates the temperature slowly to do this. Most of the time, the hot water is much cooler than 135F. At the moment it is 39F outside and the water is 116F. Even if that was being turned on and off, the expansion noise would be reduced compared with 180F water, but since it is modulated depending on outdoor temperature, the noise is very low.
If it is simple for you to use outdoor reset, I suggest you consider it. If it requires replacing a perfectly servicable boiler, it would not seem to make sense.0 -
Fin Tube Noise
Hi - You might try slipping a small piece of plastic cut out of a plastic milk bottle between the pipe and the mounting bracket. Also use plastic where the piping comes through the flooring. I was able to quiet expansion noise this way. Gerry Gill, when he built his mini tube steam system, used stainless steel wire to hang the fin tube element rather than support brackets. This makes a great deal of sense to me and I am keeping this method in reserve if I get further noise problems
- Rod0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements