honeywell VS8187A12372 WILL NOT FIRE UP

TRYINGTOLEARN
Member Posts: 2
in Gas Heating
HOW DO I TROUBLE SHOOT THIS SYSTEM? HOW MANY MILLIVOLTS SHOULD THE THERMOCOUPLE PRODUCE? WHERE CAN I PURCHASE A REPLACEMENT?
0
Comments
-
here
is a good item to read to learn..
http://www.heatinghelp.com/article/338/Boilers/266/Thermocouple-Testing-Procedure0 -
That thermocouple procedure
will not help you as what you have is a Powerpile Self Generating System. The VS 8187 gas valve by the way is no longer available as a replacement should you need it.
The pilot generator puts out 750 millivolts for starters. If you go to the "Resources" above then click "Library" and look for "Tim McElwains Closet" you will find the procedure for Troubleshooting Powerpile System. If you have to replace the gas valve a VS820A will do the job and you will have to reroute the pilot tubing to originate at the new valve.0 -
honeywell VS8187A12372 WILL NOT FIRE UP
Tim,
Thank you I have a bad pilot generator0
This discussion has been closed.
Categories
- 121.3K All Categories
- 84K THE MAIN WALL
- 2.9K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 417 Carbon Monoxide Awareness
- 40 Chimneys & Flues
- 1.7K Domestic Hot Water
- 4.7K Gas Heating
- 119 Geothermal
- 155 Indoor-Air Quality
- 3K Oil Heating
- 56 Pipe Deterioration
- 771 Plumbing
- 5.4K Radiant Heating
- 362 Solar
- 14K Strictly Steam
- 3K Thermostats and Controls
- 51 Water Quality
- 38 Industry Classes
- 73 Job Opportunities
- 17 Recall Announcements