honeywell VS8187A12372 WILL NOT FIRE UP

Options
HOW DO I TROUBLE SHOOT THIS SYSTEM? HOW MANY MILLIVOLTS SHOULD THE THERMOCOUPLE PRODUCE? WHERE CAN I PURCHASE A REPLACEMENT?

Comments

  • lchmb
    lchmb Member Posts: 2,997
    Options
  • Tim McElwain
    Tim McElwain Member Posts: 4,621
    Options
    That thermocouple procedure

    will not help you as what you have is a Powerpile Self Generating System. The VS 8187 gas valve by the way is no longer available as a replacement should you need it.



    The pilot generator puts out 750 millivolts for starters. If you go to the "Resources" above then click "Library" and look for "Tim McElwains Closet" you will find the procedure for Troubleshooting Powerpile System. If you have to replace the gas valve a VS820A will do the job and you will have to reroute the pilot tubing to originate at the new valve.
  • TRYINGTOLEARN
    TRYINGTOLEARN Member Posts: 2
    Options
    honeywell VS8187A12372 WILL NOT FIRE UP

    Tim,



    Thank you I have a bad pilot generator