Anyone get Grundfos Direct Sensors working?
thoughtfulTom
Member Posts: 18
Grundfos has a flow meter/temperature sensor product they call Grundfos Direct Sensors (there is a pressure/temp critter as well).
Resol (rebadged as Caleffi, SunMaxx, etc) BX and MX controllers can take in this data and give you BTU metering.
It is supposed to be super-cool. I've installed 6 of them, on three different projects, and not gotten successful results.
The problems range from obviously bogus data (flow at night on a drainback controller (virtually impossible - I have analog flow meters that confirm there is no flow), to more subtle problems like showing a flow that is incorrect (based on analog flow meters, and manual calculations of the increase in tank temperatures (which do not require the flow meters - so I have three ways of getting the information - two of which say Grundfos data through the Resol controller is bogus).
And the most fun: -888.8 ie the controller doesn't even recognize the sensor.
If you think I might be frustrated by these results - you are correct!
Now I did extend the wires, which Grundfos now says is not OK. So I may have caused some of these problems myself. But I have also installed using just the out-of-the-box cable and had all the problems above.
I am curious is others are having any success? (I have on installation that passes the smell test for being in the ballpark).
Feedback appreciated.
Tom
Resol (rebadged as Caleffi, SunMaxx, etc) BX and MX controllers can take in this data and give you BTU metering.
It is supposed to be super-cool. I've installed 6 of them, on three different projects, and not gotten successful results.
The problems range from obviously bogus data (flow at night on a drainback controller (virtually impossible - I have analog flow meters that confirm there is no flow), to more subtle problems like showing a flow that is incorrect (based on analog flow meters, and manual calculations of the increase in tank temperatures (which do not require the flow meters - so I have three ways of getting the information - two of which say Grundfos data through the Resol controller is bogus).
And the most fun: -888.8 ie the controller doesn't even recognize the sensor.
If you think I might be frustrated by these results - you are correct!
Now I did extend the wires, which Grundfos now says is not OK. So I may have caused some of these problems myself. But I have also installed using just the out-of-the-box cable and had all the problems above.
I am curious is others are having any success? (I have on installation that passes the smell test for being in the ballpark).
Feedback appreciated.
Tom
0
This discussion has been closed.
Categories
- All Categories
- 86.6K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 54 Biomass
- 423 Carbon Monoxide Awareness
- 98 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 102 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 66 Pipe Deterioration
- 931 Plumbing
- 6.2K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements