knightly cleaning

Options
Here are a few pics of the latest cleaning.  The amount of crud was about the same as every other year.  Wildlife residing in the burner also similar to other years.  I think one of these days I'll put an intake filter in to keep these little guys out.  The credit card got lots of use between the coils and although I probably didn't need to lightly clean the flame sensor and igniter I did anyway.  The whole process takes about 2 1/2 hours and yes, I'm kind of slow, but thorough.  Pressure washing the coil used about 10 gallons of water and my system of sucking it out with a wet vac really works well.  This system has worked flawlessly since installed in 2007. 

Comments

  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    Options
    Send that pic

    to VISA......it's everywhere you want it to be :)

    Good job on the cleaning.  Thorough beats fast any day of the week for me.

    There was an error rendering this rich post.

  • TomS
    TomS Member Posts: 62
    Options
    Cleaning

    This past summer I also cleaned my Knight and it was very similar to your pictures.  This fall when I first turned on the boiler I got a surprise as it shut down on low fan speed and the fan made an abnormal noise.  What I found was a mouse stuck in the fan impeller.  I am using a concentric vent and would like to prevent this from happening again. Anybody have any ideas on how to  screen off the intake on a concentric vent?
  • Ironman
    Ironman Member Posts: 7,376
    Options
    S.S Mesh Sreen...

    With 1/4" openings placed in the intake pipe where it connects to the concentric. Use a coupling and cut the mesh to match the inside diameter of the coupling. Let it rest against the internal stop in the coupling with the pipe holding it in place.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Steve Whitbeck
    Steve Whitbeck Member Posts: 669
    Options
    concentric

    I would lose the concentric vent. You should have at least 18 inches vertical seperation of the intake and the exhaust.
  • TomS
    TomS Member Posts: 62
    Options
    Concentric Vent Screen

    Ironman thanks for the reply.  If I understand correctly the rain cap would not be used anymore because it would not fit over the coupling.  Also, has rodent entry been a common problem with using concentric vents ?  I kind of suspect it is since you had a answer for the problem.
  • Ironman
    Ironman Member Posts: 7,376
    Options
    Wrong End

    No, I was referring to the part of the concentric that's inside the house. Cut the intake pipe 2" from the concentric and put the coupling and screen there. Don't glue the coupling; use a couple of sheet metal screws so it can be dis-assembled again when needed.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • ColoradoDave
    ColoradoDave Member Posts: 54
    Options
    Miller Moths

    Where I'm at, we have a huge problem with miller moths..... so adding a small peice of window screen to the (usually) supplied metal screen is a good idea too.  It seems the combustion air side takes the most abuse (for somewhat obvious reasons).

    With the concentric (bazooka) termination, we do it with an un-glued fitting on the combustion air take off at the termination OR do it near the boiler.  I blast of compressor air or a good seal with a shop vac can usually suck the line clear of small debris like mushed moths.
  • SpeyFitter
    SpeyFitter Member Posts: 422
    edited November 2011
    Options
    Giannoni

    Instead of using a credit card, you could also try one of those plastic dinner knives. They work pretty good.

    I believe someone (Trinity?) makes a specific water spraying mounting plate that you mount on Giannoni heat exchangers with a spray wand on it that allows you to hose out Giannoni heat exchangers.

    There was an error rendering this rich post.

  • SpeyFitter
    SpeyFitter Member Posts: 422
    edited November 2011
    Options
    Giannoni

    Double Post, whoops

    There was an error rendering this rich post.

  • Larry (from OSHA)
    Larry (from OSHA) Member Posts: 717
    Options
    I've seen those

    The trinity wand looks like a handy tool but I have been very happy using the little ball valve on the end of the hose that I have.  Very simple and it works.  The credit card is handy and flexible and won't break off in the hx so I'll just keep using it.  There really doesn't seem to be any efficiency difference between before and after cleaning, but the amount of crud isn't so much.  I suppose if the air or gas was really dirty things would be different. Bottom line, I love the boiler.  It has the best controls out there and since I do the maintenance, I'm still saving a bunch of dough.



    Larry
  • johnnyog
    johnnyog Member Posts: 1
    Options
    water balloons in exhaust cause fan failure?

    HI my knight boiler is on lockout for low fan speed. the fan speed is 0 rpm. disconnected exhaust and intake lines to boiler (concentric vent) to find peices of water balloons in the exhaust at low point near boiler outlet



    could the water balloons have travelled from exhaust vent into boiler fan?



    have to take off the fan on Friday and repair or replace, but wondering what is going on
  • Steve Whitbeck
    Steve Whitbeck Member Posts: 669
    Options
    intake

    No screen of any kind on the intake. If the wind is just right and the exhaust gasses get sucked into the intake pipe it will freeze on the screen in cold weather and this will trip the boiler out. The colder it is the more likely it will happen.