radiators half hot - traps or vents?

johnd
johnd Member Posts: 1
I was looking at two pipe  residential unit yesterday. When the boiler fired one radiator heated up very quickly (less than five minutes), but the other six radiators got warm slowly and grdaually ( more than ten minutes, and you could feel the supply pipe get hot, then the heat slowly moved across the rest of the radiator).

All of the radiators only got hot in the top half, the bottoms stayed cool. the main vent on the return seemed to be working. I'm wondering if  the problem may be at the radiator traps, or if i should take another look at the venting. 

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,516
    That one radiator

    that gets hot quickly -- in about the length of the time all of them should, in fact -- may have a failed trap.  That would do it...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • Dave in QCA
    Dave in QCA Member Posts: 1,788
    uneven distribution

    Most 2-pipe steam systems have small radiator supply pipes, usually 3/4 or 1".  This tends to create a little bit of an orifice effect and helps to even out the distribution.  Another thing that can cause problems is if a trap or traps are replaced with one that has different venting characteristics than the rest of the system.  Are your traps all the same make and model?   I recently installed inlet orifice plates to even out my 2-pipe system and was surprised when I found that one of my radiators, it a system of 32 radiators, had an orifice in it.  As would be expected, it was not heating very well.  I would advise looking in the valve of the slow radiator.   Also, there were some valves from the past that had orifices built into them.  What type of valve is on this radiator.   Pics always help!  Please post some pics of your system and the radiator, valves, traps, etc.
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com