Massachusetts oil supply line code
LittleT
Member Posts: 6
in Oil Heating
Hello
The new law for oil supply lines it needs to have a regulator valve and a protective sheath around the oil line. Can you put a sheath around the line or do you need to buy a line with the sheath already around it. I was told the inspector may want the line with the sheath already attached to it.
Thanks any help would be appreciated.
The new law for oil supply lines it needs to have a regulator valve and a protective sheath around the oil line. Can you put a sheath around the line or do you need to buy a line with the sheath already around it. I was told the inspector may want the line with the sheath already attached to it.
Thanks any help would be appreciated.
0
Comments
-
you can
either install an OSV at the tank, or run a new protected oil supply line from the tank to the burner, and it must be continuous. You can either run the copper tubing thru a non-metallic sleeve, or easier to buy the precoated oil line. The catch here is that if it needs to be done, a licensed oil tech must pull the form 1 with the fire prevention/fire department to perform the work, or if it already complies, a form 1A from a licensed oil tech is needed. Sounds like you are doing the work yourself? Unless you can get a licensed guy/girl to walk the plank for you, the work that you are doing will not satisfy the law. Have your oil company get you into compliance. You need the paper trail. Good luck To add, you only need one or the other to satisfy the law, not both new line and OSV0 -
form 1a
i thought there was only one form from the state for new mass law. the form 1a is the only one i have been using for new lines and ones that were already up to code. if there is another one what is it and where do you get it. i also did not think you had to go to the fire dept, all you had to do was give the homeowner the form 1a and they would send a copy to their homeowners insurance company.0 -
form 1a
i thought there was only one form from the state for new mass law. the form 1a is the only one i have been using for new lines and ones that were already up to code. if there is another one what is it and where do you get it. i also did not think you had to go to the fire dept, all you had to do was give the homeowner the form 1a and they would send a copy to their homeowners insurance company.0 -
form 1a
i thought there was only one form from the state for new mass law. the form 1a is the only one i have been using for new lines and ones that were already up to code. if there is another one what is it and where do you get it. i also did not think you had to go to the fire dept, all you had to do was give the homeowner the form 1a and they would send a copy to their homeowners insurance company.0 -
Form 1
is the permit to alter if the line is not compliant, and needs to be brought into compliance. As long as it is a continuous protective sleeve that the line runs thru, all is ok. It can be water line, PVC, liquid tite, etc.0 -
oil line cde
yes i know but is form 1a and form 1 the same form0 -
oil line cde
yes i know but is form 1a and form 1 the same form0 -
no
Form 1A is a form that it complies, Form 1 is a permit. Two different animals0 -
What type of plastic line
The new law requires that the oil line have a protective sleeve (or OSV). It doesn't specify what type or what standard this protective sleeve must meet or comply with.
1. What are the specs for it?
2. Does an oil line that was buried in a concrete berm (with the older type gray liner) require a change?
3. Can an oil line with a proper protective sleeve be buried in concrete berm even though it is not visible its entire length?0 -
protective sleeve
Kena, If it is a continuous non-metalic protective sleeve from the tank to the burner, you are good. It can be a garden hose, PVC, water line, etc. It must prevent the copper from coming in contact with cement or earth. It can be covered by cement as long as it is in the protective sleeve. If someone is unsure if it is a continuous sleeve, either run a new line, or add an OSV. That would need a permit ( Form 1 ). If it is determined that it already complies, your service person needs to supply you with a Form 1A. Hope this helps0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements