Coverting to gas - New boiler size question.
Speedyjoey
Member Posts: 7
in Gas Heating
I am converting from oil to gas heat. I live on long island (New York) and im looking into the Burnham ES2 boiler. My home is a HiRanch. Two zones, one on each floor. The house is about 2,450 SF. Built in 1985. I would like to know which unit to go with. Not sure how many BTUs I need.
Thank you
Joe
Thank you
Joe
0
Comments
-
Find out
how many BTUs you need. We do this with a heat-loss calculation program which takes windows, insulation etc into account.
There are plenty of contractors on Long Island who could do this for you. Try the Find a Contractor page of this site.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Thank you.
I had three people come in. One recommended a 130 BTU unit and two others recommend the Burnham ES2-5 140 BTU and the last guy say that the Burnham ES2-4 105 BTU would be good. I'm am just really confessed which unit will be best.0 -
Ask each contractor
how they determined the boiler sizing. Did they all actually do a heat loss and also measure your lineal feet of baseboard.
Find out who distributes the Burnham boiler in your area and give them the info on your house and see what they recommend.
Ask the contractors for references as to other customers that they installed this same Burnham boiler for and see if they are satisfied0 -
No
Two measured the base board other 2 just looked at the old unit. If there a way I can calculate what I would need by using the homes square feet?0 -
Budget sizing
Rules of thumb for budget sizing based on a 0 degree climate and a 70 degree set point.
R-19 Walls, R-30 Attic, Good Windows = 25 btu's a square
R-11 Walls, R-21 Attic Decent Windows = 32 btu's a square
Have no clue then 40 a square.
A betting man would put his money on that boiler quoted is oversized. Why an ES2 and not a condensing boiler? By the time you line that chimney which is required for an ES2 your in a condensing boiler price point.There was an error rendering this rich post.
0 -
Not always
if there's no safe place to vent a mod-con thru the side wall of the house, you have two choices: Either use a chimney-vented boiler, or use the chimney as a chase (if that's possible) for the mod-con's air and exhaust pipes.
The latter would preclude the use of a standard gas water heater in the same chimney, making it necessary to go with an indirect or some other type of water-heating device. This would make the job cost a lot more, possibly more than relining the chimney, so a chimney-vented unit like the ES-2 series looks a lot more attractive. And many times it's more efficient than whatever is coming out!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
thank you for your help. Just thought it was weird how they all had recommened different units
one recommended- 130K (Kenmore), two recommended the 140K (Burnham ES2-5) and the last guy said (96K Burnham P205) or the ES2-4 (105K)0 -
Would it be bad to get a unit that was a little larger?
I was thinking about getting the larger unit since it was only $150 more. Wouldnt the larger unit heat up the house faster?0 -
NO!
Unlike most things in life,bigger isn't better when it comes to boilers! Just did a heat loss on a 2900 sq/ft house in Shoreham,LI. Came out to 57K. A larger boiler short cycles and will use more fuelTo learn more about this professional, click here to visit their ad in Find A Contractor.0 -
Bob's right
a heat-loss is the only way to go- unless it's a steam system, then we size to the radiation.
But in either case, oversizing is doubly wasteful. It costs more to buy and more to operate. The only ones who benefit from this are the oil and gas companies- is it any wonder they oversize so much?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Is the the input or output BTU?
I'm still not sure with would be best: My home was build in 1984 so I assume I have some isolation. And I have two zones. and heated sf is 2410
Burnham ES2-4 105/77 (Btu in/out) or
Burnham ES2-5 140/1020 -
You need much more info than that
a heat-loss calculation considers much more than the square footage of the house.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
boiler sizing verification
Another way of sizing the boiler is trough heating degree day.
It actually gives you input for old boiler you actually used, and then you do efficiency improvement correction factor and arrive to proper size. When i get boiler size 4 times smaller then existing boiler, i do this and usually a m spot on with less then 5% difference.. do not forget pickup factor, as HDD is reflecting more steady state operation.Gennady Tsakh
Absolute Mechanical Co. Inc.0
This discussion has been closed.
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 94 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 156 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 927 Plumbing
- 6.1K Radiant Heating
- 383 Solar
- 15.1K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements