Wasting condensate
Patrick_North
Member Posts: 249
Hi all,
I've got a one pipe steam setup with wet returns. I recently replaced the decrepit wet returns and a bunch of supply piping. I included necessary valves for a pressurized blowdown, for isolating the returns (for cleaning) etc. Dan reccomends "wasting" the condensate when initially firing up a system with a bunch of new piping. This makes a lot of sense- no reason to let all that gunk and oil enter the boiler.
My question though is this: what's stopping live steam from existing this (open)condensate wasting valve? Am I missing something? Sounds dangerous.
Thanks,
Patrick
I've got a one pipe steam setup with wet returns. I recently replaced the decrepit wet returns and a bunch of supply piping. I included necessary valves for a pressurized blowdown, for isolating the returns (for cleaning) etc. Dan reccomends "wasting" the condensate when initially firing up a system with a bunch of new piping. This makes a lot of sense- no reason to let all that gunk and oil enter the boiler.
My question though is this: what's stopping live steam from existing this (open)condensate wasting valve? Am I missing something? Sounds dangerous.
Thanks,
Patrick
0
Comments
-
If
you set up whatever opening you are going to use so that the opening is at or slightly above the boiler's operating water level, the system (which is kinda dumb this way) will see a normal water level in the returns and you shouldn't have a problem.
If you do get steam out doing that, you have a different problem!Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I don't follow...
I'm having a hard time picturing this. If the valve opening (for "wasting" condensate after installation) was on the drip and above the water line and not on the return below the water line, it seems that only steam could come out- the condesate would continue down the drip.
In Dan's video on near boiler piping (http://www.heatinghelp.com/article/107/Steam-Heating/118/Steam-boiler-near-boiler-piping) this wasting port in on the return just before tying into the hartford loop. This is essentially what I have. I'm sure this isn't a "scale" drawing, but it sounds like a different approach. Jamie, does this make sense?
Thanks,
Patrick0 -
I copied the video also
The pressurised backflush is pretty straight forward. Close the Hartford valve and the system valve (s), Make some steam and watch the gauge. For me, 2 or 3 psi was enough. Then drain some sediment from the boiler. I blew out all kinds of crap. Most memorable was the handfull of 100 year old pipe threads.
I have not attempted to steam clean the returns as of yet. Like you, I would assume this needs to be done safely. I am not sure what is a safe way to do it.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements