Clear Plastic in Liquid line
TexasServiceTech
Member Posts: 1
Straight cool system.
Installed 12 years ago, serviced every spring, no major issues.
Complaint was unit freezing up.
Ambient 107
Suction pressure 19
Head pressure 325
Condenser coils clean. Evaporator coil clean. Filter Clean.
Recovered 6 pounds 4 oz R22
Removed liquid line from evaporator coil to check orifice.
Found piece of clear cellophane style plastic lodged against orifice.
Purged system with nitrogen and removed two smaller pieces of the same material.
Ran vacuum cycle and repurged system.
Pulled final vacuum and weighed in correct charge.
Called back today for same complaint.
Recovered refrigerant and opened liquid line found even larger piece of same material.
After vacuum and recharge system pressures are horrible.
Ambient 78
Suction pressure 56
Liquid pressure 208
Anyone ever had this issue before?
Installed 12 years ago, serviced every spring, no major issues.
Complaint was unit freezing up.
Ambient 107
Suction pressure 19
Head pressure 325
Condenser coils clean. Evaporator coil clean. Filter Clean.
Recovered 6 pounds 4 oz R22
Removed liquid line from evaporator coil to check orifice.
Found piece of clear cellophane style plastic lodged against orifice.
Purged system with nitrogen and removed two smaller pieces of the same material.
Ran vacuum cycle and repurged system.
Pulled final vacuum and weighed in correct charge.
Called back today for same complaint.
Recovered refrigerant and opened liquid line found even larger piece of same material.
After vacuum and recharge system pressures are horrible.
Ambient 78
Suction pressure 56
Liquid pressure 208
Anyone ever had this issue before?
0
Comments
-
Plastic
For now I would install an oversized (303) liquid line filter/drier right at the inlet to the metering device and clean it up.What could it be?0 -
Most Likely...
It came from the bag that originally contained the piston. You might want to put a drier or an inlet tube with a strainer right before the piston to catch any further debris.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Sounds Right
I would add a large suction line drier as well.....
What a crazy industry we work in!There was an error rendering this rich post.
0 -
One Other Thing...
I noticed that you said your pressures still aren't right. You might try checking the distributor with the orifice removed to see if there's any debris in it. Also, back flush the coil by feeding nitrogen in at the suction service valve with it closed. Leave the liquid line disconnected from the coil while doing this and see if anything comes out.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Is it a Rheem AC
???????0 -
Yup.......
Sounds like part of the plastic bag that the restrictor came in. Definitely back purge the evap coil and like stated above,.....See what comes out. Bits and pieces could be anywhere. If I'm not mistaken, oil and the heat generated by the compressor will degrade the plastic and may be quite difficult to get out.
Mike T.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements