New steam system
Options
ToddM
Member Posts: 13
I have a customer with a 5 section smith/mills 20. oil fired. he wants to go natural gas. I went thru the house and measured all radiators and by using the info on this site, came up with a total of 648.86 sq.ft. of radiation. Its a big old 3 story house. What does this convert to in btus?
There was an error rendering this rich post.
0
Comments
-
I'm not a pro but,
648.86 * 240 = 155726 BTUs.
Take that and add a 1.33 pickup factor and your at 207116 BTUs. Use the DOE heating capacity rating on the boiler for this. This would put you in the market for someting like a Burnham IN8.
This will not be enough if the piping is oversized or uninsulated.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
Thanks
Thanks I want to see if the supply house salesman comes up with the same thing.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 87.3K THE MAIN WALL
- 3.2K A-C, Heat Pumps & Refrigeration
- 61 Biomass
- 429 Carbon Monoxide Awareness
- 120 Chimneys & Flues
- 2.1K Domestic Hot Water
- 5.8K Gas Heating
- 115 Geothermal
- 166 Indoor-Air Quality
- 3.7K Oil Heating
- 77 Pipe Deterioration
- 1K Plumbing
- 6.5K Radiant Heating
- 395 Solar
- 15.7K Strictly Steam
- 3.4K Thermostats and Controls
- 56 Water Quality
- 51 Industry Classes
- 50 Job Opportunities
- 18 Recall Announcements