New steam system
ToddM
Member Posts: 13
I have a customer with a 5 section smith/mills 20. oil fired. he wants to go natural gas. I went thru the house and measured all radiators and by using the info on this site, came up with a total of 648.86 sq.ft. of radiation. Its a big old 3 story house. What does this convert to in btus?
There was an error rendering this rich post.
0
Comments
-
I'm not a pro but,
648.86 * 240 = 155726 BTUs.
Take that and add a 1.33 pickup factor and your at 207116 BTUs. Use the DOE heating capacity rating on the boiler for this. This would put you in the market for someting like a Burnham IN8.
This will not be enough if the piping is oversized or uninsulated.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Thanks
Thanks I want to see if the supply house salesman comes up with the same thing.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements