Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

New steam system

Options
ToddM
ToddM Member Posts: 13
I have a customer with a 5 section smith/mills 20. oil fired. he wants to go natural gas. I went thru the house and measured all radiators and by using the info on this site, came up with a total of 648.86 sq.ft. of radiation. Its a big old 3 story house. What does this convert to in btus?

There was an error rendering this rich post.

Comments

  • ChrisJ
    ChrisJ Member Posts: 15,714
    edited September 2011
    Options
    I'm not a pro but,

    648.86 * 240 = 155726 BTUs.



    Take that and add a 1.33 pickup factor and your at 207116 BTUs.  Use the DOE heating capacity rating on the boiler for this.  This would put you in the market for someting like a Burnham IN8.



    This will not be enough if the piping is oversized or uninsulated.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ToddM
    ToddM Member Posts: 13
    Options
    Thanks

    Thanks I want to see if the supply house salesman comes up with the same thing.

    There was an error rendering this rich post.

This discussion has been closed.