Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Conversion Factor?

Owen
Owen Member Posts: 147
I have EDR ratings on Fan/Coil Units, convectors and radiators from original drawings but Hoffman sizes steam traps in Pounds Per Hour of condensate.

As per Dan, I don't want to put in over-sized traps just because that's what I'm taking out.

What is the simplest way to determine the right trap?

Comments

  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,600
    Here's how.

    Divide EDR by 4 to get Pounds per Hour.
    Retired and loving it.
This discussion has been closed.