Conversion Factor?
Options
Owen
Member Posts: 147
I have EDR ratings on Fan/Coil Units, convectors and radiators from original drawings but Hoffman sizes steam traps in Pounds Per Hour of condensate.
As per Dan, I don't want to put in over-sized traps just because that's what I'm taking out.
What is the simplest way to determine the right trap?
As per Dan, I don't want to put in over-sized traps just because that's what I'm taking out.
What is the simplest way to determine the right trap?
0
Comments
-
Here's how.
Divide EDR by 4 to get Pounds per Hour.Retired and loving it.0