steam radiator replacement

Doug_45
Doug_45 Member Posts: 6
I'm going to salvage yard to replace a leaking steam radiator. How can I pressure test to check it. Any special equipment or technique? Any tips on what I should be looking for?

Comments

  • moneypitfeeder
    moneypitfeeder Member Posts: 252
    difficult?

    You would need to put a reducer in the supply (or if 2 pipe either supply or return), and then have an accumulator pump with an accurate gauge, or a compressor with a regulator on it that will measure in ounces. Then couple the source of air to the reducer (if 2 pipe, seal the other end) slowly apply the air, and spray with a leak detector solution, ie. dish soap diluted with a good bit of water. Where it bubbles it is leaking. I would check for a minimum of 2 psi, but since the safety check valve of the boiler is set to blow at 15 psi, a pro might want to see it tested up to that range. 