Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Need help in Denver, Co
George3
Member Posts: 9
I am a homeowner with a 2 pipe steam heating system that has issues - steam is slow or does not reach all the radiators. All the radiator traps in system have been replaced last year. The original boiler was replaced 10 y ago but it's piping does not make sense to me and some contractors that have seen it. The condensate return pipe connects back into the mains steam outlet above the boiler which does not make sense. Shouldn’t it go back into either the condensate tank or in the boiler but bellow it's water level where the Hartford loop is? It is also done all with copper pipes which I understand is not desirable for steam.
It seems to be hard to find a knowledgeable/experienced contractor on steam heating systems.
No one comes up if I do search in the Heating Help "Find Contractor".
Can anyone please recommend contractor in Denver Area to have a look at my system and recommend/repair what is needed.
It seems to be hard to find a knowledgeable/experienced contractor on steam heating systems.
No one comes up if I do search in the Heating Help "Find Contractor".
Can anyone please recommend contractor in Denver Area to have a look at my system and recommend/repair what is needed.
0
Comments
-
mile-high steam problems
can you post some pictures of the boiler piping for us to see?
how is the air allowed to escape from the main pipes and boiler as steam is starting to rise?
if you order some of the steam books from the shop here, it would increase your understanding of steam systems in general, and make it easier to explain things to a contractor whose own knowlege of steam may be hazy.--nbc0 -
Mark Eatherton...
Is the man I would recommend. His post are all over "the wall".Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Boiler piping photos
Thanks for you help!
In the last 2 years I already ordered few books on seam heating from this site and have been educating myself.
By searching "The Wall" with key word "Denver" I found both Dave Stroman and Mark Eatherton posting from my area.
Already contacted Dave and he was quick to respond and even looked at my system. He agreed that there is a problem with the boiler piping and is currently working on a an estimate for me.
I am posting few photos with my current boiler piping.
The system is vented at the end of the return pipe(near the ceiling above the boiler) before the condensate flows back at the inlet of the Main steam pipe. There is a second vent at the end of the Main pipe which circles the basement ceiling and returns above the boiler and flows into the condensate tank.
Your opinions are appreciated on how the return should be piped back to the boiler or the condensate tank.0 -
Well at least
someone put a Gorton #2 on that main. As for the rest of that piping- tear it out and start over. For a look at how it ought to be, go here:
http://www.heatinghelp.com/files/articles/1348/127.pdf
And if I had any money, I'd bet you do NOT need that condensate tank!All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
holy crapazoid batman!
think theres enough copper pipe on that steamer?...there must be some serious tension placed on that block when that copper header expands!..Steamheads right!..
start over..gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Near boiler piping
After looking at this system, holy crapazoid is right. The condensate tank will not needed. And someone with a briliant mind took the end of the condensate return and tied it back into the steam header! And this has been installed for 10 years and still sort of heats the house. He has had muliple "heating professionals" look at this who could not see any problems. Sort of funny that this homeowner, armed with Dan's books, knew more than than they did. If he has me do the work I will post a photo of a new dropped header. Steel of course.
Dave StromanThere was an error rendering this rich post.
0 -
Copper Crapazoid in Colorado
When I see something like this I always have the urge to want to hunt down the guy that did this installation just to ask how on earth did he decide that the boiler piping should be configured this way? Why would one possibly consider the return should routed right back into the header? Possibly "perpetual motion" steam heating?
It's also scarey that a lot of "heating professionals" didn't see anything wrong with this configuration. One thing for sure when it finally gets straightened out there will be a big improvement both from the economical and comfort standpoint.
- Rod0 -
I have the Exact same Crapezoid in Denver
I found this thread and thought I must have posted it! I live in Denver and have a boiler that was replaced about the same time, and my near-boiler piping looks exactly the same: leaky copper, no Hartford loop, un-needed condensate tank and pump. And it hasn't worked for crapola, either, in the 3 years I've had the house.
I've had several supposed experts look at it, but have gotten different answers from all of them. I am giving Dave Stroman and/or Mark Etherton a call tomorrow!
By the way, George; how did it turn out?0 -
Both by the hand of the same "master"?
Please keep us informed as to how this system improves as it is replied, and we love pictures.--NBC0 -
You might want to use the
"Contact User" feature if you want to get in touch with George. Some people drift away once we get their lives sorted out for them. We try not to take it personally. :-DJust another DIYer | King of Prussia, PA
1983(?) Peerless G-561-W-S | 3" drop header, CG400-1090, VXT-240 -
Much more better
Here is what the piping looked like when we were done. The receiver tank was removed. Now things work.There was an error rendering this rich post.
0 -
Looking good!
now go help Linum09.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Its like a brand new steam system now
Sorry for not updating you guys on my re-done boiler piping. Thanks everyone for your opinions and help. Special thanks to Dave Stroman and his guys for fixing my boiler mess in a very professional way.
After several days of initial boiler water skimming it had worked flawlessly ever since.
I have also insulated the new piping and some of the old piping that did not have insulation. Overall these improvements resulted in about 20+% lower gas bill last winter.
Some radiators that did not heat at all since when the boiler was incorrectly installed 13y. ago now in fact output so much heat that I had to turn them down. Some were in bay windows and were heating the ceiling and the poorly isolated roof above so much that last winter this created ice damming and leaks damaged my roof and ceiling. Now I am fixing my roof above the bay windows. Isn't that funny how fixing one thing sometimes leads to odd problems.
Linum09 please contact me if you need help or advice.
I know how difficult it was for me to find knowledgeable person in Denver who really understands steam systems.0 -
question
From a relative steam newbie: What's the drain in the middle of the header for?
thanks~0 -
Steam header port
The port in the middle of the steam header with the ball valve on it is for testing steam traps. We put it on per the owners request. Not a bad idea.There was an error rendering this rich post.
0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements