return,filter,comfort air blower,coil and supply trunk

That is how every central a.c. unit I ever saw was.How come my coil is before my comfort air blower and I am going to assume that is why my thermostat will not satisfy.Has anybody ever see an a.c. unit set up that way that works correctly before I confront my landlord.Thanks in advance!

Comments

  • Empire_2Empire_2 Member Posts: 2,343
    Evap coil

    Not unusual and sometimes it is where it is due to limited space.  You will also notice that the condensate is trapped or should be trapped because of the neg. draw.  The only problem is the filter.  Should be doing its job before the A/C coil.