manifold pressure at grill

Joseph_4
Member Posts: 305
in Gas Heating
I live in NYC. I had a customer ask me to install a popular name brand natural gas grill. On the grill it says it should be 4.5" water column. The set up is as follows: a 1/2 gas cock connects to a quick connect hose which has a flare hose end going into the manifold. now in a gas valve on a boiler, i understand that the valve has a built in regulator to regulate down the 1/2 psi or (14" W.c) down to 3.5 " water column. On the grill, I don't see a regulator so isn't being fed gas at 1/2 psi which is much higher than 4.5 W.C?
Thanks
Joe
Thanks
Joe
0
Comments
-
What is your
inlet gas pressure? If it is natural gas it should be around 6"W.C. out of the house regulator. If it is a low pressure gas area it can be between 6" W.C. to 10" W.C.
How may burners does the unit have? What is the required input?
Connect a manometer onto one of the orifices on one of the burners if it is a multiple burner unit and see what you have for pressure with the other burners running.0
This discussion has been closed.
Categories
- All Categories
- 86.7K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 56 Biomass
- 423 Carbon Monoxide Awareness
- 104 Chimneys & Flues
- 2K Domestic Hot Water
- 5.6K Gas Heating
- 103 Geothermal
- 158 Indoor-Air Quality
- 3.5K Oil Heating
- 68 Pipe Deterioration
- 938 Plumbing
- 6.2K Radiant Heating
- 385 Solar
- 15.3K Strictly Steam
- 3.4K Thermostats and Controls
- 54 Water Quality
- 43 Industry Classes
- 47 Job Opportunities
- 18 Recall Announcements