relocating expansion tank
petef
Member Posts: 2
Just hoping I can get some input on the location of my expansion tank and whether it should be moved - as I am planning to do tomorrow.
Buderus g124 with circ on boiler output. Installer had originally placed spirovent, expansion tank and water inlet downstream of pump.
I have been working on adding a DHW zone, zone valves, and an esbe mixing valve on return - which is done, but before I wrap everything up, it seems that my exp. tank (PONPC) should be behind the circ.
The thing is that the only way I have available to do this without major rework is to tee off of where I have my relief valve and run some 1/2" a foot or so to the expansion tank. So basically - is it permissible to have an exp tank at the output? I can't really see any reason why not, but just wanted to run it by a pro if possible. :)
Pete
Buderus g124 with circ on boiler output. Installer had originally placed spirovent, expansion tank and water inlet downstream of pump.
I have been working on adding a DHW zone, zone valves, and an esbe mixing valve on return - which is done, but before I wrap everything up, it seems that my exp. tank (PONPC) should be behind the circ.
The thing is that the only way I have available to do this without major rework is to tee off of where I have my relief valve and run some 1/2" a foot or so to the expansion tank. So basically - is it permissible to have an exp tank at the output? I can't really see any reason why not, but just wanted to run it by a pro if possible. :)
Pete
0
Comments
-
That will work...
Just make sure you don't put any isolation between the boiler and the pressure relief valve, and do not down size the connecting pipe to the relief valve.
You WILL notice a world of difference by moving the PONPC upstream of the pump.
METhere was an error rendering this rich post.
0 -
thanks Mark
all is well - probably should have moved the water inlet as well, but I've had enough.
Thanks again.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements