Old radiant system, needs new boiler
computerwhizyeah
Member Posts: 8
I have a 55 year old copper radiant system in slab of a single floor large ranch house. The present boiler is a CI sectional with one pump and a mixing valve - 238,000 btu input but needs to be replaced. I have been advised to use a Burnham Alpine condensing boiler with outdoor re-set, primary-secondary loops, etc. The owner presently changes the water temperature manually according to the season. The system will also have a indirect water heater. The boiler has been sized according to heat loss. The owner nor I do not know if the copper loops in the floor have ever been insulated. The system has always worked well for him and although in installation is not difficult, I wonder, since a lot of money is at stake for him, if there is anything about this plan that someone out there might notice to be 'out of whack'. I also have made a previous post on this subject but obviously did something wrong in sending it as it hasn't appeared on the 'wall'. Thanks.
0
Comments
-
Actually...
Any properly sized mod/con should work fine in this application. Remove the mixing valve and let the boiler control the water temp through its reset curve. Just make sure it's adjusted properly for your radiant floor.
Also, do the math to select the correct pump / speed for the secondary and assuming everything else is done with good hydronic practices, you should have a good system.Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
55 year old copper in slab
has its days numbered. beware. Many such systems have developed leaks by now.
I would begin eyeballing the "exit strategy" early so it doesn't catch you by surprise. Not to be a predictor of doom and gloom...but you should proceed cautiously.Rob Brown
Designer for Rockport Mechanical
in beautiful Rockport Maine.0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements