Combined parallel and counterflow main?
Patrick_North
Member Posts: 249
<span style="font-size:12pt">In the dreaming stages of having my steam mains repiped- the system has loads of redundant piping because the house was at one time a up/down duplex. To cut to the chase, it would be convenient to run one main as paralell flow for most of its run, drip the main, then continue another 12’ or so as a counterflow main to serve three final rads.</span>
<span style="font-size:12pt">Is this done? If so, any gotchas to be aware of?</span>
<span style="font-size:12pt">Thanks,</span>
<span style="font-size:12pt">Patrick</span>
<span style="font-size:12pt">Is this done? If so, any gotchas to be aware of?</span>
<span style="font-size:12pt">Thanks,</span>
<span style="font-size:12pt">Patrick</span>
0
Comments
-
If...
it's big enough and you can pitch it right, no reason it shouldn't work. You'll need a vent at the end of it...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
We've done it
make sure the load on the counterflow portion doesn't exceed that of the next smaller pipe size, if that size is being used as parallel-flow. And the main vent goes at the end of the counterflow portion, as Jamie says.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Dual Drips
Hi Patrick-
Someone else asked this question a few months back and it resulted in the attached drawing. Disregard the pipe sizes in the drawing as they were unique to the previous discussion.
The idea of using an individual drip at the end of each main was to prevent the condensate from the parallel flow pipe and the condensate from counterflow pipe from colliding with each other as they might do entering a single tee. Whether this is really necessary I don't know, but as it is so easy to install, the extra drip capacity can't hurt.
Just a thought for your consideration.
- Rod0 -
Here's how we did it
the parallel-flow section comes down into the tee, the counterflow section goes off to the side, and we even put in a dirt cap. The steam and condensate from the parallel-flow main travel down, and keep out of each other's way at the tee.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Aha!
Brilliant, thanks guys!
Patrick0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements