Forced h.w. zone off new steam boiler????

Paulien
Paulien Member Posts: 7
Best way to set this up w/ a NEW steam boiler? Pics. show former boiler & the zone that was existing... Any feedback from any installers out there that have had successful results?! Thanks

Comments

  • lchmb
    lchmb Member Posts: 2,997
    Like everything

    It depends. What will your new steam system be? If you go with the new Burnham Megasteam they have a specific way to pipe a HW zone off their boiler. Just simply follow their instructions and you will be fine. :)

    Are you having the install done and if so are they familiar with steam?
  • Ironman
    Ironman Member Posts: 7,531
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • Paulien
    Paulien Member Posts: 7
    Thanks

    Thanks for the tips,,have installed many a steam boiler,but never a h.w. zone off it..
  • Ron Jr._3
    Ron Jr._3 Member Posts: 605
    Staying with oil ?

    Best way in my opinion is to pressurize the zone with a coil .



    Another option is a heat exchanger .



    If the zone is lower than the boiler , I'd connect it directly to it . Gotta use a relay and aquastat to make sure the boiler don't steam if the water zone calls alone .