Low Water Cutoff switch
JohnA
Member Posts: 7
Despite my changing the water each week, the switch inside my low water cutoff ends up getting stuck about once a year. My oil company's plumber usually just shoots something like a rust remover into the low water cutoff chamber. What kind of rust remover spray is safe to use? Also, what is the white sealant he puts around the screw that provides access to this cutoff chamber?
0
Comments
-
Low Water Cutoffs Save Lives!
Hi- Below are the maintenance recommendations for the McDonnell & Miller Series 67 & 767 Lo Water Cutoff which is commonly used on a lot residential steam boilers.
The Low Water Cutoff is an critically IMPORTANT SAFETY DEVICE so shouldn't be "mickey mouse" fixed with a spray can of "rust remover"!!!
Find somebody competent to inspect and replace the defect parts or completely replace the whole unit!
- Rod
MAINTENANCE
SCHEDULE:
• Blow down weekly (at least once) when the
boiler is in operation.
• Disassemble and inspect annually. Replace
the low water cut-off if it is worn, corroded,
or if components no longer operate properly.
• Inspect the float chamber and equalizing
piping annually. Remove all sediment
and debris.
• Replace every 10 years. More frequent replacement
may be required when severe conditions
exist such as rapid switch cycling, surging water
levels, and use of water treatment chemicals0 -
More reliable lower water cutoff
Is there a good alternative to the 67/767 Series? How about a system with some kind of probe that detects the presence of water at a certain level, instead of a float that seems prone to malfunction at a fairly regular interval and requires weekly attention by the consumer?0 -
LWCO
Hi - There are basically two types of Low Water Cutoffs. One is the float type like the Mc Donald & Miller - Type 67 and the other is the probe type, like the series made by Hydrolevel. Both types require regular yearly cleaning & maintenance. The float type also requires a weekly blow down to make sure the float area remains clear of dirt and debris. Some owners prefer the probe type as it doesn’t require weekly blow downs though on the other hand , a benefit of having to do the blow downs makes sure you check your boiler at least weekly which you should do in any case. There is also a school of thought that from a safety stand point, it ‘s not a bad idea to have both types installed on your boiler. (Sort of like wearing a belt with suspenders.)
To install a probe, there must be a dedicated threaded port in the boiler at the appropriate location. On most late model boilers this is available but may not be on older models.
If you already have an automatic water feeder on your boiler, you have to be sure it is compatible functionally and electronically with the low water cutoff.
You can get Low Water Cutoffs (both the M&M Type 67 and Hydrolevel ) at Pex Supply on the internet. (They also have Type 67 replacement parts) Info on Hydrolevel: http://www.hydrolevel.com/ You probably want to get a good pro to handle the installation and setup and they can do the yearly maintenance/cleaning on the boiler/ burner at the same time.
- Rod0 -
LWCO
Thanks, Rod. The advice/information is much appreciated. I do have a professional doing yearly maintenance, but I believe they consider the Low Water Cutoff to be separate from that maintenance and therefore requiring a plumber's attention. It seems that if the manufacturer recommends a complete cleaning each year then that's what my boiler/oil company should be doing.0 -
too much fresh water
you shouldnt change your water every week. you will cause more harm then good. blow down the LWCO once a week, drain and flush once a year. always remember to bring your fresh water to steaming temperature after you refill....0 -
Question about draining vs. blowing down LWCO
What is the difference between draining and blowing down the LWCO? Either way, you are draining some of the water from the boiler, correct? Should the LWCO be drained until the water stops flowing, or simply long enough for the dirtiest water to leave the LWCO? Thanks.0 -
I expect...
that there are as many ways to blow down a LWCO as there are people doing it. But keep in mind why you are doing what your are doing: all you need to do is to get the gunk which settles in the float chamber out of the float chamber. You're not trying to clean the boiler! Therefore... the approach I personally use is to open to blowdown (boiler and water feeder OFF) until either it starts to flow in a bit of a spurt or until it is vaguely clear -- say a quart or two. Close. Repeat until the water is vaguely clear when the blowdown is first opened. If this is done weekly (less on a reasonably clean system) the total will be a gallon or two -- rarely more. Then open your manual feeder to bring the water level back up to where you want it (you did record it when you started, didn't you?), close the manual feeder and open the automatic feeder again and turn the boiler back on.
(Why do I bother to turn the auto feeder off and restore the water level manually? Because my autofeeder has a nice counter on it which tells me how much water the autofeeder has added because of losses -- and I very much want to know if I'm losing water I don't know about.)Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements