Water level
NC
Member Posts: 11
Please don't laugh! I'm on my own taking care of an old house that has steam heat. The boiler is also old - probably 25 years - and is a HB Smith. How do I add water to the boiler? The water level gauge is getting low. And, the discharge (for lack of a better word) pipe - how often should water be released from the boiler? Thanks for your help and thanks for not laughing.
0
Comments
-
adding water to steam boiler
There should be a copper pipe that goes into the bottom section of the boiler, follow that up and you will find a valve that controls the water feed to the boiler. Don't feed water into a steaming hot boiler, warm is ok as long as you feed the water in slowly. Turn that on and watch the water level in the sight glass as it fills, you want the sight glass to be about half full. It doesn't take more than 30-60 seconds. make sure to turn that valve off completely when your done.
After filling it to the correct level turn the heat up so the water boils in the boiler, that will drive off any dissolved oxygen so you don't cause any corrosion. If your still in doubt about which valve post a couple of pictures and we should be able to help you find the right valve.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Take another picture
Stand back some more. Its over to the left. By the way, you just found one of your leaks. See all that green stuff at the bottom of the sight glass. (on the brass part) That means its leaking.0 -
-
-
I'm not talking
about the water "inside the glass" I'm referring to all that green corrosion outside the glass. On the brass. The water is leaking out of the sight glass. Its leaking right where I drew the green arrow. Looks like about a quarter inch a week.0 -
leakage
Okay, yeah I see what you're talking about. Now how do I get water into the boiler?0 -
I still can't see
the valve we are looking for. You need to take the pictures from farther back. All 4 sides of the boiler, if possible. Stand back as far as you can. We will find it eventually.0 -
Manual fill valve?
That looks like it way up there. I am not 100% sure though. Can you get a second opinion?0 -
valve
I tried that valve but the water level in the gauge didn't go up. Thanks anyway.0 -
When you tried that valve
did you hear anything? Like maybe water running?0 -
fill valve
if you open that valve that was pointed out to you and water level does not rise either valve is bad there is another valve on that pipe or the glass cock which was pointed oit to you that is leaking is full of gunk and boiler water level is not showing you did not say where you live might be better if you gave a location maybe there is a steam guy who comes here that can help you0 -
Blowdown?
I probably know less about steam boilers than anyone on this web site. But it is my impression that Low Water Cut Off devices should be blown down about once a week. On this one there seems to be a shaft coming out of the LWCO with no handle on it where I would expect the blow down control to be. Do I infer correctly that this unit is not blown down regularly? Or does it have some automatic way to blow down?0 -
NC, Looks like
you need to call someone in. Thanks Ed and JDB
1a-manual fill valve doesn't work
1b-no water feeder
2a-sight glass leaking
2b-lower site glass cock might be plugged
3a-no handle on low water cutoff for blowdown
If you need someone to come over, you could use the "find a contractor" section at the top of the page.0 -
Make sure gauge glass valves are both open
The valve that Crash pointed out should be the boiler fill valve. Make sure the valves above and below the sight glass are fully open (full ccw) so they will "see" the boiler water level.
When you open up the fill valve you should hear water flowing through it and the water level in the sight glass should slowly rise. If you don't hear water flowing when that valve is open then you have a problem further up the line.
I agree you should have someone look at this system to install a blow down handle and fix the leak on the lower part of the sight glass. that lower sight glass leak might just need the bonnet nut tightened up a bit but don't go to far or you will crack the glas tube.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Valve
Yes, I did hear water running when I turned that top valve.0 -
blowdown
In the box that you highlighted there is a hex screw (along with a wrench) . When you turn the screw, rusty water is discharged from the pipe. That should be done often? How do I know when to close it? Will water run clean eventually?0 -
contractor
Intersting....there's no contractor (from this site) within a 100 mile radius!!0 -
The low water cutoff
is supposed to be blown down every week or so during the heating season, and once in awhile during the summer. Most, if not all that I have seen always have a yellow handle, like the one in this photo. Yours, for some reason has been removed.
Exactly which city and state are you located in?0 -
Water cut-off
I'm in Vermont.0 -
blow down -- how much?
The blow down should happen once a week during heating season, like they said. For me, I do about 1 quart or two a week -- it's not too good to have to remove larger quantities of water from the system than needed, since then you eventually will need to replace it, and introducing more fresh water than can be helped can lead to other issues. So the flushing of the blowdown is meant to keep the crud from glunking it up. If you have not done it in a while, maybe a little more at first, maybe a gallon or more to flush things out the first couple of times, see if it gets clear(er). But I would not do that until you figure out how to get water feeding back in the system! Probably, that'll simply take some hard looks at the water supply piping and tracing it to see how it connects and where there are valve to open to let the water in to the boiler system.0 -
How far up in Vermont?
Maybe something could be arranged I could make a trip to the Green mountains.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Take Charles
up on his offer, unless you are north of Montpelier -- it would be worth it.
I'm concerned that you say that you hear water running when you open what does look to be a manual water fill valve -- but that you don't see a change in the gauge glass. That running water sound suggests that water is going somewhere... and you need to know where! You also need to know how much water is in that boiler... and it sounds as though you really don't know...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Steam Books
Hi NC - It sounds as though your boiler needs a good going over by a steam pro.
If it is practical, I’d get Charlie Garrity as he is very experienced with steam.
Don’t be embarrassed about asking questions . Most of the homeowners on here have been in the same position as you at one time or another and have learned by asking questions.
There are also some really good books on residential steam heating available on this website in the “Shop” section at the top of the page. I would recommend starting out with “We Got Steam Heat!” It’s written for the homeowner who is new to steam and contains a lot of information , diagrams and explanations. It’s easy, humorous reading and in a few evenings you’ll be light years ahead in your knowledge of steam heating. Here is a link to the book:
http://www.heatinghelp.com/products/Books/5/61/We-Got-Steam-Heat-A-Homeowners-Guide-to-Peaceful-Coexistence
I’m sure you have more questions so don’t hesitate to ask them.
- Rod0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements