Main Vent Calculation
jamesylove
Member Posts: 6
I have no main vents in my single pipe steam system. I have two mains - a 45 ft run and a 24 ft run. I've removed sheetrock and have found a spot for the main vents, but would like some assistance on how to calculate the optimal number of main vents.
For a 45 and 24 ft run (1 3/4" pipe), how many Gorton #2s would you recommend on each main?
Thanks for the help.
For a 45 and 24 ft run (1 3/4" pipe), how many Gorton #2s would you recommend on each main?
Thanks for the help.
0
Comments
-
I'd use a Gorton #1 on the short main
and a #2 on the longer one.
If you want to use all #2s, use one on the short main and two on the long one.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Tapping into main
Any recommendations on drilling/tapping into the main? I do not have room to insert a tee, so I'll have to tap it. Is a 1/2" tap sufficient?0 -
Yup
that'll work fine. Just make sure you angle the tap up slightly from horizontal. This will angle the pipe upward a bit so water won't collect in it.All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 75 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 93 Geothermal
- 150 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 921 Plumbing
- 6.1K Radiant Heating
- 373 Solar
- 15K Strictly Steam
- 3.3K Thermostats and Controls
- 50 Water Quality
- 39 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements