Vacuum steam heat system problems
RBrower
Member Posts: 9
I own a house built in 1930. It has steam heat. The original boiler was
old, big, and in need of replacement.......but it did work to heat the
whole house. (Kitchen, living room and dining room downstairs, 3
bedrooms and 1 bath upstairs)
I had a local HVAC company replace the boiler a year ago. Since then the
front half of the house gets no heat (living room and the 2 bedrooms on
the front half of the house) while the other half works great (Dining
room, kitchen and bed/bath on the back half)
The company that installed it spent hour after hour and service call
after service call trying to fix it. They haven't been able to get it
right yet. I even coughed up an additional 2000.00 over the original
contracted price because I felt sorry for the owner.
The owner of the company attributes the problem to the fact that my
system is a "vacuum" system and no one knows how to work on those any
more, and all the guys who DID know are all dead (that's why they are
called 'deadmen')
Any suggestions on how to get heat to the rest of the house?
Thanks
Bob
old, big, and in need of replacement.......but it did work to heat the
whole house. (Kitchen, living room and dining room downstairs, 3
bedrooms and 1 bath upstairs)
I had a local HVAC company replace the boiler a year ago. Since then the
front half of the house gets no heat (living room and the 2 bedrooms on
the front half of the house) while the other half works great (Dining
room, kitchen and bed/bath on the back half)
The company that installed it spent hour after hour and service call
after service call trying to fix it. They haven't been able to get it
right yet. I even coughed up an additional 2000.00 over the original
contracted price because I felt sorry for the owner.
The owner of the company attributes the problem to the fact that my
system is a "vacuum" system and no one knows how to work on those any
more, and all the guys who DID know are all dead (that's why they are
called 'deadmen')
Any suggestions on how to get heat to the rest of the house?
Thanks
Bob
0
Comments
-
You should
post some pictures here, and have the system identified. We need photo's of the radiators, and the boiler area. Also some pics of how the boiler hooks up in the ceiling, and how the smaller pipes come down from the ceiling and go back to the boiler.
Once it gets identified someone will be able to let you know what, if any, changes need to be done.0 -
Vacuum Systems
Hi Bob- Vacuum steam systems are/were the "Cadillac" of the steam systems. As "Crash" mentioned, post some pictures of your new boiler and of the radiators especially including the piping/fittings where it connects to the radiators. Also post pictures of any "odd" contraptions that are located on the piping. All these will help us to better identify the make/model of your vacuum system and to give you some ideas as to what needs to be adjusted to make your system work properly.
Some of the best steam heating pros in the U.S. are active on this site and quite of few of them are experts on vacuum systems. Tell us where you are located and maybe we can recommend a steam pro close to you.
You might also want to get some of the excellent steam books available in the "Shop" section of this website. I would recommend to you "The Steamy Deal"
http://www.heatinghelp.com/products/Super-Deals/14/129/A-Steamy-Deal
This consists of three books. They are written for the homeowner who is new to steam heating. They are humorous, easy reading and are filled full of diagrams, facts and pictures. In a few evenings of reading you will be "light years" ahead in your knowledge of steam heating. Read "We Got Steam Heat!" first as it is a good introduction to steam heating and the terminology of steam. "The Lost Art...." describes how different steam systems and their components work and includes a big section on vacuum systems.
- Rod0 -
Yes,.....
Follow Crash's advice. There are lots of folks here that work on Vapor/Vacuum systems. About 1/2 to 3/4 of the two pipe steam systems I work on are old vapor/vacuum systems and they work very well. They are quite common in building built before WWII.There was an error rendering this rich post.
0 -
Photos of my vacuum steam heat system
Hi Guys,
Thanks for the responses to my post.
I'm attaching some pix of the system before and after renovation. the only 'plumbing' that was changed is that going into the new unit.
on the registers that do NOT work; the 3/4 inch inlet line gets warm UP TO the radiator but the heat doesn't make it across.
If a schematic diagram will help let me know and I'll map it out and attach as well
Thanks again
Bob0 -
That sure looks like
a Trane Orifice Vapor system.
In such a system, there are no traps or air vents at the convectors. An orifice, cast into the convector element's inlet header, keeps steam from completely filling the element and getting into the dry return as long as you keep the pressure low. Air and condensate go into the dry return, the air is vented and the condensate returns to the boiler. It's the height of simplicity.
What make was the old boiler? I've never seen one like that. The new one doesn't look like it has a proper header, equalizer or Hartford Loop, so it will need to be repiped. Those Peerless 63-series steamers have 3-inch tappings for connecting steam lines, and this is the size you should use, especially on a Vapor system.
Where are you located?All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Photos of my vacuum steam heat system
If you blow up the pic of the back of the old boiler you can read:
American Radiator Co
Max W.P. Lbs.
Steam 15
Water 30
At one point the tech said he had the pressure up to 12 PSI. I see the Vaporstat looks like it's set at 12ish OzSI......could he really have meant PSI?
the convectors have no valves on them.
Do you need more pics?
If the old unit worked well, why would the new unit need to be repiped? And why would 1/2 the house be working well now, and not the other?
I'm in Middletown, NY0 -
It looks to me
as thought that nice new Peerless sits a good deal lower than the old boiler (what was it? That's a neat looking boiler!). Which gives rise to a possibility: in the section was doesn't heat any more, is there somewhere a drip from the steam line down to a wet return? And a nearby drip from the dry returns which I see there, also to the wet return? And is that wet return still wet? Or does the new boiler sit low enough so that the wet return isn't wet any more -- in which case you could be getting steam going down that drip and back up into the dry return. Presto, no heat.
Just a thought... but look all over the basement for booby traps.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Hartford Loop
One more thing:
When the salesman, and later the company owner looked at the system, they both said it had a Hartford Loop and explained how it worked (which I've forgotten by now)
If you need better or more specific pics let me know
Really appreciate the help
Bob0 -
Greek to me
Wow.........that is all absolute Greek to me.........
I wouldn't know a wet return if it sat on my lap and called me Papa
How would I know?
I remember the tech telling me that the steam arrived on one end of the radiator and condensed as it cooled, returning to the boiler as water........that's about all I know
The old boiler was an American Heating Co. product.
The owner added some decorations of his own.
Bob0 -
Flared copper is a bad sign.
I am thinking you need to use the find a contractor section up top of the page. The basics are whats the pressuretrol set at? why are the returns so high after they drop? How did they size the boiler?Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Contractor help
Hi Charlie,
I agree; I'm going to have to have someone look at the system and make suggestions so I can contact the installer and have them make it right.
The salesman 'sized' the boiler by measuring the house and consulting a table.
Looks to me like the Vaporstat is set at 12 OzPI but have no idea what the return is or why it's high or even what the heck that means.
but thanks for your input
Bob0 -
The convectors needed to be measured not
not the house. The boiler maybe too small to fill the house system with steam.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
I bet Jamie has it......
I bet those return lines on the right of the boiler were wet before and I am nearly sure they are dry now. If the pipes dropping down from the ceiling just to the right of the boiler are the ends of the steam mains, this is probably part of your problem.
Also, the new piping connecting the boiler to the system is incorrect. I am not sure what size boiler you have, but the piping looks pretty small...check you installation manual for the proper size. The size listed are inside diameter so add about 1/4 inch for the outside diameter. The connection from the new horizontal header pipe above the boiler to the system needs to be off the top of the pipe not the side. The old boiler had a 45 degree elbow here which is less than optimal but much better than the new piping.There was an error rendering this rich post.
0 -
If it's any orifice system, boiler sizing can be different.
Sizing the boiler to the heat load is very possible with two pipe systems, especially an orifice system.There was an error rendering this rich post.
0 -
Hey Boiler Pro
Soon as I hit Submit I knew you would be here. As always glad to get your input. I live in the world of one pipe steam. I still think it may be a bit small for the system.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Dear RBrower
Please tell us where you are located so we can possibly recommend a good steam man nearby.
In the meantime, do either of those Gorton #2 main steam vents get hot while the system is heating up?All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
Bob, looks like your old green boiler was a big hit!
Must be spring, or The Pro's finally got an hour off, all at the same time. There must be a hundred years experience here advising you on what to do to get some heat to the other side of the house. You can tell those guys that hooked up your new boiler that, The Deadmen ain't dead, they are alive and well.0 -
Location and steam vents
Hi Gordo,
I'm in Middletown, NY
All 4 of the large round steam vents get hot while the system is running
bd0 -
If the Main Vents on Your Dry Return
Are getting hot and shutting off, steam is getting where it should NOT.
If the the main vents on the ends of the steam mains are getting hot and shutting off, that's ok.
Steam supply mains should have steam in them when the system is running.
Dry returns (returns above the boiler's water line) on a two-pipe system should only have air and a little water in them.
If there is steam getting into your dry returns, it will tend to block the release of air from other heating units and they won't heat.All Steamed Up, Inc.
"Reducing our country's energy consumption, one system at a time"
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Baltimore, MD (USA) and consulting anywhere.
https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc0 -
I think Jamie nailed it.
other than the boiler isn't piped right, look at the drip pipes by the chimney..look how high they are compared to the water line of the new boiler..then look at the water glass height from the original boiler..have them lower the returns or build a false water line..AFTER they repipe the boiler properly.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
-
that helps alot..
well done..pictures worth a thousand words.gwgillplumbingandheating.com
Serving Cleveland's eastern suburbs from Cleveland Heights down to Cuyahoga Falls.0 -
Final solution?
Hey guys,
Is that the final solution? the new boiler needs to be raised so the water level in the sight glass is the same as the old one?
On Fri night I e-mailed a contractor from the "find a contractor" at the top of the page. Hopefully they'll contact me during the week
Thanks for all the info
Bob0 -
I would lower
the returns. The new pipe will help with flow.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
too late to fix?
Another question:
After fighting with this thing during the entire winter of '09-'10, about this time of year the installer told me it was too late to continue, and he would start again when the weather got cold during winter of '10-'11.
He said the returns need to be cold so the steam would condense.......and with warmer weather the pipes would not be cold enough.
This seemed a little fishy to me at the time but..........is he correct?0 -
Your new installer
is likely going to have to start from scratch. Disconnect everything, gas, water, electrical, steam supply and return, and the chimney. Possibly rotate the boiler a quarter turn clockwise. Its not going to be as simple as lifting the boiler to match the waterline of the old one.0 -
Steam condenses...
at 212 Fahrenheit. In the radiators. If you have steam condensing in the returns, you have big time problems -- which, other than the water line and near boiler piping problems, I don't think you have. And if your radiators or returns are so hot that the steam doesn't condense, you also have big time problems... !
Your installer, I'm sad to say, appears to not have a clue as to how steam heat works...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
He is lucky enough to have dry returns
this means the boiler stays the pipes drop. If the boiler was across the building from where the returns connect then other things could be done. But lets KEEP IT SIMPLE. Jamie said in a nicer manner all you need to read about your installer's excuses. I love repiping Steam boilers in the warm weather, means I can work 8 hour days and go home for supper instead of 14 hour days and packing two meals a day. Bunk! is all I can add about his reasoning.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
my two cents
Have the valves on the radiators been replaced? if you are getting heat up to the pipes and not in the radiator itself it is due to pressure. the coin valves must be replaced every 5 years or so on these type of systems. the steam is compressing the air to create enough pressure to not allow the steam to flow into the radiator. when those valves are operating properly they let the air out and the when the steam makes it to the outlet the bi metal shuts it and traps the steam in the radiator. each valve orifice must be sized properly in order to produce even heating. the radiators farthest away must have the largest orifice to allow a lower pressure so the steam will travel the distance required. the orifice on the radiator in the room with the thermostat should always remain small so that all of the other radiators receive the steam and produce the heat required before the thermostat can be satisfied.0 -
plumber
the quick vents are not correct if this is a vacuum system and the boiler is not plped correctly at all0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements