error codes

rockd
Member Posts: 1
E21 error code on peerless purefire boiler. This code keeps coming up , not much experience with residential boilers. We mainly do big commercial, can someone help?
0
Comments
-
The E-21 on that
boiler indicates that the 120 VAC polarity is reversed. Has any electrical work been done? If you google Peerless PureFire it will bring you to there I and O manual with all the different codes and procedures.0