Changed from Del .85/80B to Hago 1.10/80B, now gets small puffback at startup
cwilliams2000
Member Posts: 140
So in an effort to resolve a small carbon buildup problem on the F4 bruner after about a month of good running operation I went with Peerless's recccomenation for the WBV-04 and installed the Hago 1.10/80B. Installed it, checked Z, S, electrodes are right on, good fuel supply and new filters.
Installed the Hago and now every start if you are next to the boiler you catch a small puffback smell, no noticeable smoke, but just enough to smell it which wasn't happening before.
Decided to recheck all measurements again and everything appears correct. I haven't used Hagos before, always Delevans with no issues. I also noticed that their was oil on the nozzle and base when I removed it. The tube is new and the nozzle was correctly torqued so I am wondering if posibbly the nozzle could be bad.
The burner is an AFG with the cleancut pump and genesys control with a 15 sec prepurge. It is a soft sounding clean light so no booms or other loud issues. Maybe Hago is not as good? Any ideas would be appreciated
Chris
Installed the Hago and now every start if you are next to the boiler you catch a small puffback smell, no noticeable smoke, but just enough to smell it which wasn't happening before.
Decided to recheck all measurements again and everything appears correct. I haven't used Hagos before, always Delevans with no issues. I also noticed that their was oil on the nozzle and base when I removed it. The tube is new and the nozzle was correctly torqued so I am wondering if posibbly the nozzle could be bad.
The burner is an AFG with the cleancut pump and genesys control with a 15 sec prepurge. It is a soft sounding clean light so no booms or other loud issues. Maybe Hago is not as good? Any ideas would be appreciated
Chris
0
Comments
-
What are the combustion.....
...readings now, compared to the Delavan?There was an error rendering this rich post.
0 -
Hago/Delavan
A Delavan "B" in a blue tube is a solid nozzle. A Hago in a blue printed tube is a Semi-Solid nozzle. They aren't the same.0 -
Nozzles:
Hado Solid nozzles have either a black cap or a green cap.0 -
Hago
It is a Black Cap Hago Solid, not the semi-solid0 -
I forgot the other thread
but why are you upsizing the nozzle? And why Hago instead of the Delavan?0 -
Excess air?
What was your CO2? Sounds like a combustion problem. Did you adjust for the higher firing rate?0 -
right on
You were right on, was a combustion problem, way to much air resolved and set correctly and she is running great. Thanks0 -
Combustion Testing
Amazing what you can learn with combustion testing. Good on you for having a tester and knowing how to use it.
And there's all those out there who don't own them but don't need them because they have such "a good eye", they can tell by just looking at the fire. I wish I had developed that "eye" after all these years.
Maybe if you work at it long enough, you won't need a combustion tester and will develop "an eye" like them. Keep using the combustion tester until you develop it and can be like those guys. I haven't developed it yet. After 40+ years, I still haven't.
Amazing what you can find out from calling Tech Support.0 -
me too ice.
After all these years of looking at flame, I still can't do it. But I have a 28 yr old journeyman that apparently can.
Yeah Right.0 -
I've always
started off by eye, and fine tune with testers. One has to know what a good fire looks like as opposed to a bad one.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements