lowering hot water temp
eappleton
Member Posts: 111
Our hot water at the tap is very hot (170 degrees). I'm trying to lower it to 130 or so. I'm I'm pretty sure I can use the hot water tempering valve at the juncture of the cold and hot water lines to do this, but there is a scary tag on it that seems to say it can't be used to control the temperature at the tap:
"Watts Hot Water Extender Tempering Valves cannot be used for tempering
water temperature at fixtures."
The tempering valve says hotter and colder on the top. Can I just turn this screw counterclockwise? What are the warnings about?
(the installation document for the valve is attached.)
"Watts Hot Water Extender Tempering Valves cannot be used for tempering
water temperature at fixtures."
The tempering valve says hotter and colder on the top. Can I just turn this screw counterclockwise? What are the warnings about?
(the installation document for the valve is attached.)
Single-pipe steam | 24 apartment, self-managed coop | Federal FST-40 Scotch Marine boiler | Carlin 701CRD burner | Heat Timer EPU-CH | Honeywell pressuretrols | Heating oil #2 (20% bio)
0
Comments
-
Intriguing question
Did you try adjusting it per the manual you posted?
To change the temperature of the water, loosen the Lock Nut to
free the Adjusting Screw. Turn clockwise to attain cooler water
and counterclockwise to attain hotter water. A full turn of the
Adjusting Screw is equal to approximately 10°F. Watts recommends
that a temperature gauge be installed on the tempered
line and be checked at least monthly under normal flow conditions.
The gauge may be installed in the tempered line at least
6 ft. away from the tempering valve.0 -
There is a reason...
why Watts puts that scary label on (and it's not just to make the lawyers happy). When there is no flow, the valve sense that the water is cool, and it adjusts itself to try and warm the water up -- by opening the hot water side all the way. Then, when you turn on the tap, you may get a slug of fiercely hot water before the valve can react to temper it. Depending on exactly where the valve is in relation to the fixture(s) (farther away is better) and the piping in between, this may or may not turn out to be a concern.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
This discussion has been closed.
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements