Steam Problem
BWeaver
Member Posts: 9
Hello,
I have a steam system that is blowing steam out the vent pipe on the condensate pump box.
What can I do to fix the problem?
I already cleaned the steam traps the best I could. Any other ideas.
Also what should the steam pressure typically be?
I have a steam system that is blowing steam out the vent pipe on the condensate pump box.
What can I do to fix the problem?
I already cleaned the steam traps the best I could. Any other ideas.
Also what should the steam pressure typically be?
0
Comments
-
Second question first...
(it's a lot easier) -- the cutout should be between 1.5 and 2.0 psi. If you have the typical pressuretrol, set the front scale at a bit above 0.5. The differential, which is added to the front scale, is probably set at 1 -- it's the white wheel inside the pressuretrol.
Lots of reasons why you might be getting steam at the condensate pump box, mostly having to do with either failed traps or a water seal somewhere which isn't sealing anymore. It shouldn't happen. But, to help further, we really need some photos or diagrams of how the boiler is piped, and how the mains and returns are set up, and how condensate gets to the condensate pump box.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
probably a failed trap ...
as Jamie mentioned, it's probably a failed trap .. close/open each radiator one by one until the steam stops downstairs .. if the steam never stops, you have more than 1 failed trap. how big is this system and do you really need the condensate pump?1-pipe Homeowner - Queens, NYC
NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph
installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains
Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
my NEW system pics | my OLD system pics0 -
Steam at condensate pump
You're right in figuring you have problems with your traps. The problem is, if your system is like most I've ever seen, you've got more than one failed, and trying to replace them piecemeal will end up costing more than you think, as one bad trap can ruin a brand new trap pretty quick by letting steam pressure jump from the supply to the return. Thermostatic radiator traps are fairly easy to check (by temperature drop), but you may also have end of main F & T traps which may have failed as well-which aren't as simple to diagnose. In any case, if you have steam at the pump, you need to stop it-the pump won't last long otherwise.
As for the pressure set-point, it ultimately depends on your application. You didn't mention whether it was process or comfort heat, or whether you have a pressuretrol or vaporstat with either additive or subtractive differential-that will determine what the settings will be.0 -
More info & questions
The steam boiler is a Burnham V9 5 section. The unit heaters all have traps, but the cast iron wall heaters only have thermostatic valves. It has honeywell pressuretrol controls.
It is being used in a comercial application i.e. an old fire hall. It is a 2 pipe system.
Another question how much temp drop should be between supply and return pipes?
And is it possible to clean the traps out and get them to work again. also can the castings rust through on the inside?0 -
answers, comments, etc
You say the cast iron radatiators have only thermostatic valves. No traps? Are you sure there is not a thermostatic trap on the outlet? If not, are they piped directly back into the return? That should not be. Maybe you meant that the radiators have only thermostatic traps?
Pressure drop between supply and return. There should be no pressure on the return. The return should be at atmospheric pressure. That is why the condensate receiver is vented. If all of the traps are working, you would not have steam at the receiver, or anywhere in your return piping.
Generall, F&T traps (float and thermstatic) can be repaired. The cast iron bodies, while they may form a rusty film on the inside, generally will last 50-100 years. The float, set, thermostatic element, etc., are another matter. They are generally repairable.
This is a link to Hoffman Specialty page on type H F&T trap. http://www.hoffmanspecialty.com/pdf/hs900/Hs900-h8.pdf
This ia a link to Hoffman Specialty page on type 17c Thermostatic trap. http://www.hoffmanspecialty.com/pdf/hs900/HS900-17C.pdfDave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Thermostatic Valve or Trap
I'm not sure if it is just a valve or a trap however it does not have a float mechanism.0 -
Thermostatic valve vs trap
A themostatic valve is on the inlet of the radiator. It is adjustable, and it opens and closes the steam valve based on room temperature.
A thermostatic trap is on the outlet of the radiator. It closes with the presence of steam and does not allow the steam to pass through it. When steam is not present, it allows for both air and condensation to pass.
Check out the links I posted for Hoffman products, it would give you an idea of what you're looking at.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
temps
What should the temp diffence be from the supply pipe to the return pipe?0 -
Depends on the trap
Usually around 30 degrees F.
Here is a link to a page that may be helpful to you regarding steam traps.
http://www.bellgossett.com/Press/BG-lowsteam.aspDave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
Another Question
What kind of chemicals would be best for this boiler? Maybe an all in one?0 -
Manufacturer's Recommendations
You should refer to the manufacturer's recommendations before using any additives to your boiler. Normal operation of cast iron steam boilers does not require any chemical additives unless you have abnormal and corrosive water conditions.
Did you get your traps fixed?Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0 -
chemicals
I have parts ordered for the traps. I used a temp gun & feel rather sure which ones are bad.
Burnham recommends using a treatment recommended by a local water treatment guy.0
This discussion has been closed.
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements