manual reset pressuretrol

On a system that has a pressuretrol set to cut out at 1 1/2 psi, what should the manual reset be set at?  I have it set at 5 and someone in the building is saying that it's set too high an that it should be at 3.

Comments

  • Jamie Hall
    Jamie Hall Member Posts: 24,852
    Five seems OK...

    It is, after all, a safety backup.  Three might be a little better -- thinking of possible problems with traps and vents -- but on the other hand, these things are a little flaky and the last thing you want is for it to trip before the regular one does, at oh dark hundred hours and 10 below zero.  So I'd leave it at 5 and not worry about it.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • George J.
    George J. Member Posts: 25
    Yes

    That is the exact reason why I raised it to five.  It was set at 3 and the pressure on the guage does get to 2- 2 1/2 psi even though it's set at 1 1/2 and I didn't want a no heat call.  Also it is not regulating the pressure in the system, it is just a safety device.  Thanks.
  • George J.
    George J. Member Posts: 25
    Yes

    That is the exact reason why I raised it to five.  It was set at 3 and the pressure on the guage does get to 2- 2 1/2 psi even though it's set at 1 1/2 and I didn't want a no heat call.  Also it is not regulating the pressure in the system, it is just a safety device.  Thanks.
  • jpf321
    jpf321 Member Posts: 1,568
    you may want ...

    to install a L408J1017 vaporstat and/or get a good low pressure gauge on there to see what's going on .. of course you've already cleaned the pigtails and the pressuretrol intake orifice right .. 
    1-pipe Homeowner - Queens, NYC

    NEW: SlantFin Intrepid TR-30 + Tankless + Riello 40-F5 @ 0.85gph | OLD: Fitzgibbons 402 boiler + Beckett "SR" Oil Gun @ 1.75gph

    installed: 0-20oz/si gauge | vaporstat | hour-meter | gortons on all rads | 1pc G#2 + 1pc G#1 on each of 2 mains

    Connected EDR load: 371 sf venting load: 2.95cfm vent capacity: 4.62cfm
    my NEW system pics | my OLD system pics
  • George J.
    George J. Member Posts: 25
    Yes

    Yes and the pigtail is new.